baldelectrician

-
Mentor
Esteemed
Arms
Reaction score
1,430
We don't normally do PV, however I was called to a PV inverter with no power, 6 years old

Found supply OK, however fed through a AC type RCD.

PV inverter has power, no display etc, no fuses blown

Supply Zs OK, voltage at strings (about 260V in afternoom, east west split)

DC and AC isolators present, no SPD on AC or DC sides

No internet, online possibility option - does this affect choice (do some operate online only?)

What would you recommend as a 3.68kW / 4 kW replacement?
 
No of panels, wattage of panels, no of strings will also be needed to choose, you can overdrive the inverter a little, Solis have a good range for that size, some are 1 string some are 2. Internet not needed but is used for app for client to view. Setup is via inverter panel.
 

Reply to Recommend a replacement inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
At work we've got an 8 panel single string set up, going into a 3000w inverter via a double pole DC isolator. The AC goes supply > isolator >...
Replies
11
Views
3K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock