- Reaction score
- 1,437
We don't normally do PV, however I was called to a PV inverter with no power, 6 years old
Found supply OK, however fed through a AC type RCD.
PV inverter has power, no display etc, no fuses blown
Supply Zs OK, voltage at strings (about 260V in afternoom, east west split)
DC and AC isolators present, no SPD on AC or DC sides
No internet, online possibility option - does this affect choice (do some operate online only?)
What would you recommend as a 3.68kW / 4 kW replacement?
Found supply OK, however fed through a AC type RCD.
PV inverter has power, no display etc, no fuses blown
Supply Zs OK, voltage at strings (about 260V in afternoom, east west split)
DC and AC isolators present, no SPD on AC or DC sides
No internet, online possibility option - does this affect choice (do some operate online only?)
What would you recommend as a 3.68kW / 4 kW replacement?