Existing double gang socket in the corner of a kitchen on a dedicated 12m length above ceiling 2.5 final circuit to CU, was used for a WM and a tumble dryer protected by a 32amp MCB.

I wish to keep this arrangement but on lifting floor boards above ceiling I noted entire run of cable/s was not in good shape with dings in the cable sheathing so will want to replace.

As mentioned existing is a double gang, surface mounted socket, can this socket arrangement remain or should it be two single sockets?

If double socket can remain should the circuit be a 2.5 ring or should I increase to 6mm T&E radial?

Socket/s, dedicated circuit will only be used for WM and separate TD but more often both WM and TD will be in use at the same time.
 
And 4mm cable.

Put it on a 32A breaker. (Rcd protected, of course)

There is a chance it would overload at 16A, if both machines hit a heating cycle at the same time
 
And 4mm cable.

Put it on a 32A breaker. (Rcd protected, of course)

There is a chance it would overload at 16A, if both machines hit a heating cycle at the same time
It's is a GE CU, fully populated, split load with EB61 B series mcbs, it is an old board although in good condition, I can't find an RCD to fit, not even sure if GE made one for this board.

If I run a radial 4mm T&E cable to 2 x RCD single sockets with 32amp mcb at CU end, would this be safe and ok?
 

Existing double gang socket in the corner of a kitchen on a dedicated 12m length above ceiling 2.5 final circuit to CU, was used for a WM and a tumble dryer protected by a 32amp MCB.

I wish to keep this arrangement but on lifting floor boards above ceiling I noted entire run of cable/s was not in good shape with dings in the cable sheathing so will want to replace.

As mentioned existing is a double gang, surface mounted socket, can this socket arrangement remain or should it be two single sockets?

If double socket can remain should the circuit be a 2.5 ring or should I increase to 6mm T&E radial?

Socket/s, dedicated circuit will only be used for WM and separate TD but more often both WM and TD will be in use at the same time.

It's is a GE CU, fully populated, split load with EB61 B series mcbs, it is an old board although in good condition, I can't find an RCD to fit, not even sure if GE made one for this board.

If I run a radial 4mm T&E cable to 2 x RCD single sockets with 32amp mcb at CU end, would this be safe and ok?
I have now taken a good look at the CU, it is split load, 100amp main switch and a 80amp, 30Ma RCCD fitted.

As I will be replacing the existing 2.5 final with a 4mm radial to two seperate single gang sockets on an existing 32amp MCB, is there still a requirement and/or necessity for me to source and swap to a RCD as there is a RCCD fited?
 

Reply to Dedicated double socket or single sockets for washing machine and a tumble dryer. in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
222
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
792
Hello there, we are wanting two new double sockets in our kitchen, one will be below counter to accommodate gas hob and ovens ignition plugs...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock