Hi, I have always made sure my installs have no departures from bs7671 but I'm doing a ccu change next week and have done some preliminary testing and the heating circuit (boiler and heating controls) has low IR readings, had a look in all obvious places and cant find any problems, had trouble breaking the circuit up as its a bit messy, client has just decorated so he doesn't want any damage to the house, seeing as its all fixed equipment (I'm unsure on the cable routes but id guess its buried less than 50mm at some point) is it acceptable to leave this circuit unprotected and note it on the departures section? all the earthing/bonding is mustard. Any experience on this would be appreciated, thanks.
 
firstly, what was the IR reading for the heating circuit? secondly, the cable buried <50mm deep -- if it's going to be RCD protected, then no problem. don't forget that the IR would need to be under 10KΩ to cause RCD tripping.
 
Hi, should have explained, I have a rig I made up I use sometimes, its basically an rcd adaptor that I wire into and plug into a socket, when I did this it tripped, the IR reading was bouncing around I think it settled around 7Mohms across all points, I remember it was the exact same number. The reason Im asking is, I want to know if its acceptable to leave it off the RCD side if I have to, as I don't think I can leave them with no heating at this time of year, can I note it as a departure as the cable is probably less than 50mm deep
 
at 7MΩ, i wouldn't worry. BS7671 quotes 2MΩ as a minimum, so just RCD protect the circuit.better still, fit a RCBO in the non RCD section of the CU.
 
thanks for your response but im not worried about the circuit, when I put it on an rcd it was tripping straight way, so I don't want to RCD protect it, I want to put it on an MCB with no rcd protection.
 
then there's a fault on either the circuit or the heasting system. does it still trip with the boiler out of circuit?
 
Just as a reminder departures from BS7671 are only cases where the circuit is not designed to BS7671 but is still safely designed, it is not a non compliant situation, which is what you are describing (circuit requiring RCD protection not RCD protected because of a fault on the circuit).

That said if you are changing a CU you only need to ensure that the circuits you are reconnecting are safe for continued use (which may well be dubious in this case) not that they meet current regulations.
I would do as Guitarist says, tell them they need that fault rectified before changing the CU.
 
thanks for your response but im not worried about the circuit, when I put it on an rcd it was tripping straight way, so I don't want to RCD protect it, I want to put it on an MCB with no rcd protection.

So...Would you sleep soundly at night knowing that you had connected this known-faulty circuit to the non-RCD side so that the fault wouldn't show up? Daz
 
Hi, I have always made sure my installs have no departures from bs7671 but I'm doing a ccu change next week and have done some preliminary testing and the heating circuit (boiler and heating controls) has low IR readings, had a look in all obvious places and cant find any problems, had trouble breaking the circuit up as its a bit messy, client has just decorated so he doesn't want any damage to the house, seeing as its all fixed equipment (I'm unsure on the cable routes but id guess its buried less than 50mm at some point) is it acceptable to leave this circuit unprotected and note it on the departures section? all the earthing/bonding is mustard. Any experience on this would be appreciated, thanks.
what do you want?...a round of applause?
i had this down as standard...
 
New posts

Reply to Departures from bs7671, certification. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Eh up :) I've done some new PDF forms for BS7671 18th Edition Amendment 2 2022 (the Big Brown Book), based on the IET model forms. You can fill...
Replies
27
Views
12K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
764
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock