Search for tools and product advice,

Discuss Derating a BS3871 following an EICR C2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi, I’m interested to hear other views on BS3871 MCBs being changed following a C2 non compliance on an EICR for over rated protective device. Eg. A 2.5mm radial circuit protected by a 32A device and then swapping the BS3871 for another BS 3871 but a 20A device.
 
If it is a fixed load of 20A-ish or less it might be fine, subject to end of circuit Zs being able to meed ADS time.

Otherwise (e.g. socket outlets so unknown load profile) it ought to be down rated to 20A or 25A depending on the method(s) along the length of the cable.
 
So starting from the top.
I’m looking for general thoughts rather than a particular installation. But to keep it simple I’ll use an example I’ve come across. MEM 32A Type C feeding a radial socket outlets, singles in trunking and conduit with flush floor box. Located in a public area of a shopping center for pop up traders to use. A direct and approved MCB is not available in a 60898 or RCBO to 61009. Old stock 3871 are available from national wholesaler, but would you agree that fitting this then changes the design of the circuit ? My question is if available would you or would you not fit ?
 

Reply to Derating a BS3871 following an EICR C2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
5K
So I have just swapped over to using fusebox as my go to brand for CUs and I noticed they stock a 25A RCBO…mmmmmm do any of you use these a great...
Replies
3
Views
2K
Hi everyone, Looking for honest opinions on C2 ratings on a recent EICR. Terrace house probably built 1930's, rented out. Not sure if this is a...
Replies
14
Views
4K
I just have a question about the RCCB seen in the picture below. It is a 63A RCCB protecting the 32A shower circuit, 32A cooker circuit and 2 x...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock