Hello,

I wonder if someone can help me here.

My understanding is :

Leading edge dimmers are suitable for mains GU10 halogen lamps, but need to be down rated 75 to 50% to cover the load.
Leading edge dimmers are not suitable for GU5.3 / Mr16 low voltage lamps.

Trailing edge dimmers are suitable for both GU10 halogen and MR16 (with electronic transformers) and don't need to be down rated.
Trailing edge dimmers are preferable to leading edge as they have soft start and overload protection.

My questions are:

Are there common characteristics where you can identify a trailing vs. leading edge dimmer by looking at it ?
I see that some trailing dimmers have a slight L shape to them (the bottom of the L containing the coil), but this doesn't seen to be universal.

I recently replaced a 400watt dimmer which was controlling 9 x 50w mr16s.
The dimmer looked like it's been there a long time, and looked to be leading edge (not L shaped).
obviously, when I installed the new trailing module it went into protection mode,
until I removed 1 x lamp, bringing it down to 400 watts.
i advised the client to replace the lamps with 35W ones to give some leeway and allow him to replace the 9th lamp.
The client didn't do this and dimmer failed after 2 weeks.
This seemed strange as it wasn't overloaded and in a 35mm backbox with space.
But may have overheated as it's a two gang dimmer.

My thought is to down rate the lamps to 35W a piece and replace the 400W trailing dimmer (400w iQ Push on / Push off Dimmer Switch Module)

Am I just plain wrong in thinking you can't use a leading edge dimmer on Low voltage lighting, say a 1000w module for this arrangement ?

I think the client would be happier if he could stick with 50W lamps.

Any advise would be appreciated.

Thanks a lot,

Alex
 
me dad used these for dimming 100,000watt searchlights , 1943
4226415636_c562e3518e_z.jpg
 

Attachments

  • 20140503_002620.jpg
    100.2 KB · Views: 65
dunno where the puppy came from. must have pressed a wrong --- somewhere.
 
Yeah, you can't beat a random dog post once in a while and it's good to see you're taking care of your nails Tel. :28::winkiss::sailor:
 
You have the information about dimmers correct, generally electronic transformers will need a trailing edge dimmer to control the dimming properly.
You cannot really tell by looking what type of dimmer it is, unless it is labelled leading /trailing edge!
Having a dimmer at maximum rating in a double dimmer situation will probably have pushed the dimmer into overheat, a lot of them have protection and will recover after a while, but would not be suitable for continued use.
A more complicated resolution, and more expensive, would be to replace the 12V lamps/transformers with 230V dimmable LED lamps and an LED dimmer.
 
Thanks for the helpful post Richard,

I have a Selectric (?) 1000watt dimmer,
I'll give them a call tomorrow to confirm they're suitable for LV lights
and install it on Tuesday.

If it fails I'll advise down rating the lamps and go back to a Varilight 400watt dimmer
running under maximum.

Thanks for the posts... and the puppy photo : )

Al
 

Reply to Dimmer Selection Wisdom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I currently have 4 JCC LED down lights in my bathroom with a 2 gang dimmer on the outside. The first dimmer switch controls the LEDs and...
Replies
6
Views
2K
As the title says, I am looking for a trailing edge smart dimmer. I have gone through 3 smart dimmers already, only to read here tonight that all...
Replies
3
Views
2K
Having a bit of a nightmare with what should have been a simple job. Back in January I replaced some old Varilight dimmers which had failed after...
Replies
6
Views
1K
Ok, so i purchased an Airbus A320 Reading Light from the cockpit and i want to convert it to a desk lamp that runs off standard mains. The...
Replies
14
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock