Discuss Dimming options/systems options in the Lighting Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
I need to install 2x 600x1200 led grid fittings into a small office.

The occupant needs to have the option of dimming the light levels because of the nature of her work.

IV found a couple of fittings but not sure how I source the correct dimming option. Domestically, anything I have installed with a dimming function has just relied on the switch itself dimming the fitting. All the fittings iv found so far have DALI, 1-10v, switch dim, push button dim.

My question is, do you have to have these systems in place to use one of the options above? We use DALI here so I know that system has to be installed but unsure of the others.
 
And a 1-10v dimmer switch, do they usually require a neutral?

No, the 1-10v signal is on a seperate pair of conductors.

You can get 1-10v dimmers which also incorporate a switch for the 230V supply or else you would usually need a seperate switch to turn the fittings on and off.

It's not obvious from the picture but this one from aurora switches the 230V supply by pressing the knob and gives a 1-10v signal by rotating the knob. 1 Gang 2 Way Rotary Dimmer - http://auroralighting.com/gb/ProductDetail/AU-DSPLED
 
So with a 1-10v fitting and a 1-10v switch, all I'd need to do is connect a control pair between the 2?

I'll just need to check I can physically connect a pair between the 2. It's a suspended ceiling so chances are the switch wiring will dissapear in conduit somewhere :mad:
 

Reply to Dimming options/systems options in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
190
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
730
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
602
Good morning all. I have an issue with some dali lighting. Basic system as far as i can tell. Dimmer, controller and 8 button switch. No other...
Replies
9
Views
5K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock