I think I got it: There was a faulty MCB which did not open when operated manually*, causing the porch light circuit to stay on unexpectedly. This, and a remembered similar observation by the homeowner, created a suspicion that some false connection existed bypassing something in the CU.

Various tests were undertaken involving the supply which naturally was still live, so live tests were used instead of dead. During these experiments, an erroneous assumption was made about the significance of the voltage reading to a disconnected conductor, which along with low but not significant IR readings added to the suspicion, which was the subject of the thread.

Along the thread, the apparently innocent RCD was dragged in as another suspect as it had not tripped while the suspected fault existed. In fact there was no reason for it to do so but this was not realised due to not having calculated I=V/R.

Am I close?

* This is unusual and nasty. I would like to know more about this aspect.
Yes that sounds about right , thanks
 
Ok guys old post I know.....maybe not much to do with the origional post...more to do with the neutral earth fault not tripping the rcd/rcbo...I had been led to believe that this will be the case unless you use the type with the white earth reference lead..eg schneider
 
New posts

Reply to Disconnected Neutal Still Showing Connection To Neutral (somewhere) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock