Hi all, I've just been asked to disconnect a 3 phase compressor. Not having done this before is it just a case of power off, disconnect then power back on or is there something special I'm missing out or need to consider?
Regards.
 
find where the 3ph compressor is fed from. isolate it. test dead at the copressor, check your tester on a known supply, and check dead again. disconnect compressor. I would perosnally lock the isloator off, if it has one. If not, and it is fed straight from the board, then i would personally disconnect the cables also from the breaker.

If you are still not sure, than ask someone to assist you Ie supervisor, or more experienced sparks
 
If it purely electrical then you just need to disconnect and make the circuit safe.

If responsible for the air side then you need to make sure that the system is not pressurised before you start undoing couplings and sorts. Though most will have non return vlaves fitted, not rote that they work. So turn off and normally there are ball valves on the accumalator which you open that will vent the air. Don't worry if you get a little water as well, as that will be normal.
 
Cheers Johnboy, that's exactly what I expected so no surprises there. Just thought that there might be something extra that I needed to take into consideration that I was over looking. As I'm recently qualified and starting out as self employed this will be the first invoice I've ever sent out. My question is a daft one but do you charge VAT on labour?
Regards.
 
your spot on johnny but I stupidly enough thought he was as he asked the VAT question. Then realsed as soon as I sent it that the chances are he wasn't

So to clear up if your VAT registered then you do have to charge VAT on labour
 
Just one to note chaps,

I have heard that the way they calculate to see if you should be paying VAT may be no longer down to yearly turnover.

The limit will be divided into 12 and if you exceed the monthly allowance three times in a row then you will need to be registered.

All word of mouth at the mo tho.
 
find where the 3ph compressor is fed from. isolate it. test dead at the copressor, check your tester on a known supply, and check dead again. disconnect compressor. I would perosnally lock the isloator off, if it has one. If not, and it is fed straight from the board, then i would personally disconnect the cables also from the breaker.

If you are still not sure, than ask someone to assist you Ie supervisor, or more experienced sparks

Tut tut, you know thats not the done way anymore ;)
 

Reply to Disconnecting a 3 phase compressor in the Australia area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
616
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi, leading on from my question the other day about running the 3 phase compressor off my 8.5kW generator I have since got my hands on a 240v to 3...
Replies
0
Views
882
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
299
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock