Hello people,
I'm designing switchgear for a residential estate, of about 60 houses, specifically the protection for the incomer. Is there any provision in the British Standard that advises on diversity for such a large number of household units?
 
In the UK most DNO's allow 2 or 3 kW per dwelling as long as there is no electric heating.
so 60 x 2 = 120. the next up standard size of transformer is 200kVA.
Can’t imagine electric heating will be a requirement on this one ?
 
No, but air-con may be an issue. I know the OP says that they use British standards but I think there will be a big difference between a standard UK house and a Kenya one.
 
No, but air-con may be an issue. I know the OP says that they use British standards but I think there will be a big difference between a standard UK house and a Kenya one.
Yeah, thanks a lot for this, the weather is not too extreme here and the cold and warm days are tolerable without electric devices.
I was thinking on the lines of say, NEC 220.84, if there's any document in the British Standards that may be an equivalent.
 

Reply to Diversity Factors in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Replies
3
Views
1K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
278
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
778
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hi all, I posted here some time ago asking for validation of a quote I received for a rewire. (10k assumed 60 points) And got some good advice so...
Replies
2
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock