Discuss DIY: Wiring a Sonoff T0UK1C smart switch. in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
2
DIY Advice required. Ive just recently brought a Sonoff T0UK1C wifi smart switch for my Living Room. The existing light switch is ya standard one way switch with live/neutral connected (No earth wire connection - therefore earth is isolated). How would I wire the Sonoff switch in replacement of my existing light switch. The Sonoff smart switch comes with Neutral in, Live in, and I shall assume (Live) out. I attemtpted to wire earlier. Neutral wire to the Neutral In, and Live to Live in. This causes a leakage with my light as the LED (non smart) in my fitting were on (but dimmed) so I suspect some form of live leakage. I switched live wire on the smart switch to (Live) out but lights did not come on (assuming that this was because there was no circuit completed to supply power to lights). Would anyone know the correct configuration for this smart switch with a single Neutral/Live wire - Is the earth wire required in some way with this smart switch - although I have a feeling it isnt. Ive attached an image of the smart switch. Many thanks!
 

Attachments

  • 20221103_133427.jpg
    190.4 KB · Views: 9
Hi. Welcome to the forum. The new switch requires a neutral connection. When you say you have a light switch with live and neutral, I suspect what you actually have is a live and a switched live, not a neutral. Could you post a picture of the wiring to the existing switch?
 
  • Like
Reactions: DPG
Ahhh right! I did suspect that but went with the live/neutral combo. Yeah sure. I'll add an image on my next reply.
 
Thanks for the pic. You see the small piece of red sleeving on the black wire? That means the black wire is a switched live, not a neutral. Which means unfortunately you cannot use that particular smart switch in this situation. Unless you add another wire to the circuit, which is probably better done by an electrician.
There are smart switches that don't require a neutral connection.
 
  • Like
Reactions: DPG
Oh bummer. Yeah after you said I most likely had a live/switched live with no neutral I was starting to suspect this. Im assuming i CANNOT add capacitance directly to the smart switch. I've just done a quick search on amazon and found some No neutral smart switches on there. I knew I should have looked a bit more before buying this one.
 

Reply to DIY: Wiring a Sonoff T0UK1C smart switch. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
462
Hi, i’ve been trying to buy a smart switch 1 gang 1 way but i opened my conventional wall switch and i only have 1 red wire(Live Old UK) 1 black...
Replies
3
Views
534
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
723
littletwinn
L
Hi. I am trying to replace a heating timer with a smart switch. The current timer is the type with a dial on the front and 1 to 24 written on it...
Replies
2
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock