Discuss DNO Isolation For Changing DB in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi All,

I need to change a DB in a block of flats in central London (W2 postcode), where EDF can't give a date for at least 6 weeks to come and isolate the supply, but at the same time won't / can't give out a date after this, which makes no sense to me!
This is both options of just popping around and isolating until work is done or installing a smart meter with DP switchgear!
The supply is a standard 1361 Type II fuse, and i'm not too keen on cutting the tags!

Does anyone have alternative methods of isolating the supply so as to change the DB? Also what is the average cost nowadays for this?

TIA
 
EDF are an energy supplier you need to contact the DNO for the region you are in. You might get a better response. Ask them if you can do it yourself as well. Sometimes they are OK with that and even give you temporary seals. I do know a number of sparks carry their own seals. Not that I am suggesting anything untoward. Energy suppliers do not isolate the DNO equipment the DNO do, while the DNO do not touch the energy suppliers meters....usually. No absolute rules on this but that seems to be general etiquette/legal position.
 
I don’t think I have ever met or worked with a sparks who have waited for the supplier to remove the cutout fuse,

the only jobs where the supplier has been needed to come to site is to either move a meter or replace a busted head
Had a chat with a DNO man about this and he was of the opinion that so long as nothing untoward happened they turn a blind eye.

I've got a service head change booked for Friday, will be installing an isolator while they're at it.

Quite looking forward to watching them.

The cable is a three phase PILC and they intend to do the change of head live by chopping the cable in the street, changing the head and the jointing the cable.

What could possibly go wrong ?
 
EDF are an energy supplier you need to contact the DNO for the region you are in. You might get a better response. Ask them if you can do it yourself as well. Sometimes they are OK with that and even give you temporary seals. I do know a number of sparks carry their own seals. Not that I am suggesting anything untoward. Energy suppliers do not isolate the DNO equipment the DNO do, while the DNO do not touch the energy suppliers meters....usually. No absolute rules on this but that seems to be general etiquette/legal position.
Thank you Vortigern,
I tried UK Power Networks initially, but they said I need to arrange with EDF. They both seem to be extremely busy with this "new normal" and possibly playing off on each other, in my view!
 
arrange with EDF
Speak to the supervisor and raise a complaint if necessary. That is nonsense. DNO deal with cut-out, energy company deal with meter and ne'er the twain shall meet, except sometimes. Sometimes you do have to insist and persuade. Frankly I would do it myself unless the cut-out looks too old or dangerous. If it was a dodgy cut-out then you could force the DNO to action. You say a block of flats, am I to understand each flat has a cut-out? Or is there a cut-out for all the flats with a ryefield board or some other isolator at the source?
 
If it’s any help - today I worked in a flat in an older block of 4, with 3 phases and 5 supplies taken. Fuse seals appear to have been left in the mess in the bottom of the cupboard...
 
Speak to the supervisor and raise a complaint if necessary. That is nonsense. DNO deal with cut-out, energy company deal with meter and ne'er the twain shall meet, except sometimes. Sometimes you do have to insist and persuade. Frankly I would do it myself unless the cut-out looks too old or dangerous. If it was a dodgy cut-out then you could force the DNO to action. You say a block of flats, am I to understand each flat has a cut-out? Or is there a cut-out for all the flats with a ryefield board or some other isolator at the source?
It's an old converted block
Speak to the supervisor and raise a complaint if necessary. That is nonsense. DNO deal with cut-out, energy company deal with meter and ne'er the twain shall meet, except sometimes. Sometimes you do have to insist and persuade. Frankly I would do it myself unless the cut-out looks too old or dangerous. If it was a dodgy cut-out then you could force the DNO to action. You say a block of flats, am I to understand each flat has a cut-out? Or is there a cut-out for all the flats with a ryefield board or some other isolator at the source?
It's a converted block. 3-Phase feed to 3 singles for each flat. The blocks are in good shape, where one of them has the tag already cut, who's to say that the previous person didn't cut this one too ;)
 

Reply to DNO Isolation For Changing DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I've turned up at a job where the tenant needs to change the DB as the face is falling apart and was cut to fit more RCBO modules. Anyway...
Replies
24
Views
2K
An interesting phone conversation with my own electricity supplier (Good Energy) which was very disappointing, and made me sigh (professionally)...
Replies
23
Views
9K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
S
Both Basic & Fault Protection SELV – if anything is provided by SELV, this gets a tick, otherwise N/A. Examples would be 12v extractor fan or 12v...
Replies
1
Views
7K
S
Hello all I am new to this site and i am glad i have found it as it looks crammed with useful advice from people in the know. I am not too...
Replies
1
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock