That was my thinking, system had periodic inspections and the initial verification.

Job was planned by the bosses, timing and planning not up to the electrician.

Advice to next shift on at 8am to test critical systems given. Client happy to wait a further 4 hours. They neither tested nor re-energised. Left no power for 2 days.

When it was tested... and re-energised... no bang.

Has caused a bit of a thing at work. Just wondering which way to go.
 
That was my thinking, system had periodic inspections and the initial verification...

...Has caused a bit of a thing at work. Just wondering which way to go.

The reason given for not doing anything was there was a C3 fault. The board installed was smaller than the original so conduit no longer fitted. (Not installers choice) it was planned to be boxed in. This was predicted and reported to management. Knockouts were given grommet strip edging.

Tbh... I'd have tested it, powered it up and said get the joiner in ASAP. (I think the 2nd shift are just bullying the original electrician)
 
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
 
Last edited:
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
Yes we used to run some galv trunking horizontal butted up to the board and take the conduits into the trunking which means no gaps or mis-aligned old conduits in the new DB
 
To explain the situation... it's 4am, The electrician has been working since 8am.

So the Electrician has been working continuously for 20hrs and is then starting or completing a C.U change?

Powering up untested because it's inconvenient / potentially a H&S issue is not a valid reason.
It could be a bigger H&S issue if there was a fault that caused injury or worse.
Just because it had had previous inspections doesn't mean at the end of the CU swop that it doesn't have any faults, especially given how long the Electrician had been working.

There's already a serious H&S issue with the electrican working 20hrs.
 
Last edited:
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?

Agree. Conduits line up perfectly. There's about a 9-10mm gap. It's boxed in with no stress or strain & no access. Essentially the conduit is rendered null & void?
 
So the Electrician has been working continuously for 20hrs and is then starting or completing a C.U change?

Powering up untested because it's inconvenient / potentially a H&S issue is not a valid reason.
It could be a bigger H&S issue if there was a fault that caused injury or worse.
Just because it had had previous inspections doesn't mean at the end of the CU swop that it doesn't have any faults, especially given how long the Electrician had been working.

There's already a serious H&S issue with the electrican working 20hrs.

Ok... maximum security prison. Various high risk prisoners topping themselves and stabbing each other... yes planning should have been way way better... but loss of power was a real H&S risk. Refusing to test it or put it back on for 2 days over a C3 fault? The more I think about it the more I think they should have had the guys back and sorted something out.
 
I still don't get how the job ended up going the way it did. Was it badly planned? Were there too few staff doing the job?

What if it had gone wrong due to lack of time/testing?

Edit: I realise it's easy for me to criticise while I'm sat here drinking Old Peculier!
 
Last edited:
I still don't get how the job ended up going the way it did. Was it badly planned? Were there too few staff doing the job?

What if it had gone wrong due to lack of time/testing?

As far as I can tell mistakes on both sides. Electrician thought 6-8 hours to install and test. Had to put in extra metal conduit for fire alarm because board had to be moved further left to align the conduit. Board supplied had incomer on wrong side and most CPD's supplied were wrong too. True nightmare job. The bosses son organised it and was assisting (office admin/wannabe apprentice) apparently he just sat down and did next to nothing. Didn't even pass tools.
 

Reply to Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like...
Replies
4
Views
8K
W
Hello again ladies and gentleman, To those who vaguely remember who I am from my last posts maybe 24 months or so ago and those who of course...
Replies
8
Views
1K
wade88
W
G
I'm taking C&G 2377 22 next year probably around May ish My hunch is that asking some qualified electricians a few somewhat daft questions...
Replies
20
Views
5K
goodconnection
G
S
Hi everyone, I am after some advice/feedback on the British gas six weeks electrician course in Rotherham . I was told it will cost £3995 inc...
Replies
25
Views
3K
sedgy34
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock