Carlos_tlewis

Hello!

Just a quick question, had a look but can't see anything about it.

Basically my customer wants 1 Socket and 1 Light in their garage, the garage is joined to the house.

What I'm use to doing is running a cable from house consumer unit to garage consumer unit and then running sockets and lights off that.

So my question is, do I need to install a consumer unit for the garage or can I just take the cables from house consumer unit.

The house consumer unit is a split load board so everything will be RCD protected.

Might seem a daft question but would be great if someone could clear it up for me, thanks in advance!
 
Hello!

Just a quick question, had a look but can't see anything about it.

Basically my customer wants 1 Socket and 1 Light in there garage, the garage is joined to the house.

What I'm use to doing is running a cable from house consumer unit to garage consumer unit and then running sockets and lights off that.

So my question is, do I need to install a consumer unit for the garage or can I just take the cables from house consumer unit.

The house consumer unit is a split load board so everything will be RCD protected.

Might seem a daft question but would be great if someone could clear it up for me, thanks in advance!

No reason not to extend the lighting and ring final to include the garage.
 
Doesn't have to have it's own garage CU, If there's no great load being used I'd feed into a SFCU, then out to socket, FCU down again for the light.
 
or, if there's a spare way in the CU add a 16A or 20 MCB , then 2.5mm radial to garage socket, then 5A FCU for light. the FCU can double as a switch for the light.
 
Or, if it's easier, create a new 20A radial from an RCBO on the non rcd side to feed the socket and use an fcu for the light. Has the advantage that the house remains on when clint runs over the mower lead.

If you can keep all the cables surface mounted, forget the RCBO and use an RCDSO
 
If there's no great load being used I'd feed into a SFCU, then out to socket, FCU down again for the light.

and this

FCU can double as a switch for the light.
I have done this for garage/conservatory, esp. when the house is wired to 16th Ed. (ie. no RCD on lighting), and fed the garage/conservatory from the RCD side.

On one job the building inspector insisted that I wired the lighting circuit in 1.5mm, in case someone replaced the 5A lighting fuse with a 13 A one.
 
Last edited:

Reply to does garage need consumer unit? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
905
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
764
Hi can you power a second consumer unit in the garage from our main consumer unit. We have a big armed cable from the main consumer unit into the...
Replies
14
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock