So if we can just slap in single up front RCD boards, what is the point of the reg in question AND why did we all start putting in dual RCD boards

Just wondering ?
 
Nope, I think the suggestion is the designer must divide the circuits across RCD's, so that any anticipated earth leakage would be limited to 30% of the tripping current for the RCD, i.e. 10mA for 30mA RCD. So consideration of the appliances and loads connected to said RCD. Kitchen appliances and IT equipment come to mind.

Westy proceeds me. See why its important to read & comment on the draft. You've got 3 days left.

I thought it was 25% so 7.5mA.
I haven't got regs book in front of me so I may be wrong
 
It is a new Reg in the 18th Ed draft, 10% of the rated residual operating current of the device.

Thanks for that westward. I've checked your post #30. That's interesting to know.
I've now got my books out( 17th edition that is) and I still cannot find where I've think I've seen 25% of rated residual current as a design guidance. Therefore a 30mA rcd should be designed with7.5mA as its max.
I know I've seen it somewhere.

I'm wandering where the 30% 9mA came from.
 
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.
 
I believe some guide books may quote this figure as it is some "rule of thumb" rcbos are prone to unwanted tripping once a 25% threshold of their rating tripping current is reached.

Really .............. not sure I believe that.

So how do you estimate the anticipated earth leakage of any device then?
 
Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
I am only quoting a rule of thumb I believe may be quoted in a commentary/guide book which is what Paignton Pete has probably seen and stuck in his mind. 25% equates to 7.5ma for a 30ma device and it does ring a bell in my head that this should be used as a basis for circuit design. It may have some substance with the proposed 18th Ed quoting 30%.

Edit, see #57.
 
Last edited:
Thanks for that westward. I've checked your post #30. That's interesting to know.
I've now got my books out( 17th edition that is) and I still cannot find where I've think I've seen 25% of rated residual current as a design guidance. Therefore a 30mA rcd should be designed with7.5mA as its max.
I know I've seen it somewhere.

I'm wandering where the 30% 9mA came from.
Okay this is bugging me so if you have a 16th Ed copy with Section 607 in it check out Regulation 607-02-03 there you will find it.
 
I'm sceptical about that much leakage current flowing in a healthy circuit too, unless there's a heck of a lot of I.T. equipment all going at once.
 
Are you sure, all RCBOs ? If that were the case they'd all fail the half rated current 'no trip' test and therefore be no use at all.
The aim here is to keep the currents at a happy level to prevent unwanted tripping, ideally an rcd/rcbo should trip under fault conditions and not excessive leakage when there is no fault. By quoting a percentage level you allow some leeway for further accumulated current and all should be good. Design a circuit where levels are excessive then any further accumulated current may result in unwanted tripping.
 

Reply to Does this comply with 314? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
530
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
724
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
836
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
813
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock