Discuss Does this look like an earthing issue? Meter readings attached in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi folks. I am regularly experiencing tingling shocks from my laptop and kettle. Both of these things are plugged into something with a ground plug.

I decided to measure the neutral to earth voltage, at least for the nodes I can reach at my plug. I see significant AC voltages measured between the ground pin and the neutral: maybe 90 V or so. I'm not sure in this house wiring which pin is line and which is neutral, but I've included photos of four relevant measurements in this post.

I would have expected one of these measurements to come out low: perhaps 0-10V AC. Instead, they all look like either our nominal 240V here in Rwanda, or some point halfway between line and neutral.

Does this seem like an earthing problem? Also, could this indicate significant imbalance in my area, which the utility should do something to correct?

Also, if I do provide a solid earth between the panel ground and physical earth, can I expect a pretty big neutral current? I'm inviting an electrician to my house (as I am an electrical engineering professor but know my limits and respect technicians) but curious what you folks think, and thanks for your attention to a first time post!
 

Attachments

  • WhatsApp Image 2020-11-25 at 13.09.14.jpeg
    54.6 KB · Views: 39
  • WhatsApp Image 2020-11-25 at 13.08.40.jpeg
    56.9 KB · Views: 37
  • WhatsApp Image 2020-11-25 at 13.08.00.jpeg
    61.4 KB · Views: 37
i would say that you have no earth. can you use a long lead and measure resistance from earth terminal on a socket to the main earthing terminal.
 
Agreed, your initial diagnosis is correct, the resistance to earth is so high as to be in the same order of magnitude as the input resistance of the meter and the reactance of the cables' stray capacitance at 50Hz. Something is disconnected somewhere.

I would vary Telectrix's test to say first measure the voltage between the offending socket earth and main earth terminal, and then measure the resistance only if it is found to be minimal. The latter being to prove that the connections on that part of the wiring at least are sound.
 
Thanks @Lucien Nunes and @telectrix . I'll first see if I can find a long lead. Actually, first I have to confirm that there is an earthing terminal *somewhere* in the house. I found the breaker panel, and I expect somewhere near that should be a main disconnect. It's likely in the attic, where the service enters the building. So it will be a pretty long lead! Will be careful and keep you posted.
 

Reply to Does this look like an earthing issue? Meter readings attached in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
Hi all, Replaced a ceiling light yesterday (I'm a novice but confident with basic electrical work). All was well and working, so I turned off...
Replies
13
Views
1K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
3K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock