Discuss Does Wylex RCCB meet Regulations? in the The Welcome Forum area at ElectriciansForums.net

Electron

-
Arms
Reaction score
20
A customer wants a house refurbished. Attached is a photo of the existing Consumer Unit. three circuits are protected by an RCCB (an old type of RCD) and two aren't. I have recommended a new Consumer Unit with full RCD protection. Is there any way the existing can be made to conform?

DSC_1298.JPG
 
An RCCB (residual current circuit breaker) is not an old type of RCD. RCCBs are still manufactured today.

RCD is a generic term for all types of residual current devices including RCCBs; RCBOs; SRCDs; PRCDs etc. Dual RCD boards are DBs which contain two RCCBs.
 
The old wylex RCDs are to BS4293 and would still meet the requirements of the regulations even though the standard is now withdrawn; subject to satisfactory testing.
They tend to trip faster than new ones!
If the house is being refurbished then a new consumer unit would seem very sensible as it would be an easy way to ensure compliance.
The options with the existing would be to move everything onto the one RCD which is not generally a good idea, or provide external standalone RCD protection for the two unprotected circuits which would be acceptable but hardly neat for a refurbished house.
 
Only a FOOL would try and retain that very old fuseboard.

Your answer to the client is a simple one - a refurbishment means a new fuseboard - and possibly a full rewire.

Moving all the circuits onto 1 RCD isn't an option either IMHO
 
A lovely board, straight mcbs, blank plates that only come out when the cover is removed and aside from the plastic hinged lid, metalclad. Did you know Wylex do retrofit metalclad covers to fit existing NSB boards which have metal back boxes but plastic covers.
 
if you are altering any circuits, they must then comply with current regs. replacing the CU to provide RCD protection for those 2 circuits is the preferred, but not tho only, way.
I would also try replace the fuseboard; but they'd have to get rid of that spider first :eek:
never seen spider wiring?
 

Reply to Does Wylex RCCB meet Regulations? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
751
Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Replies
8
Views
338
Had a customer message me before I went to do a job asking if I could put a new bulb in a spotlight while I was there, so I picked up some LED...
Replies
5
Views
384
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock