Discuss DOL starter and switches in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

munga42

Hi,

I have a Dol starter which i would like to use for my single phase irrigation pump. The Coil on the contactor is 240v. there are 3 lines in L1 L2 L3. It is connected to a 17 - 25 amp overload. I know that I have to link the wires together some how, T1 to L3?? There is a start button on the top but its not connected to anything, 13 & 14 N/O?

The idea would be to link in a pressure switch to stop pump when the travel sprinkler comes to the end of its run. Also within the water tank I would like a float switch that would cutout the pump when the water is low. I would like a solenoid water valve to be activated when the float switch stops the pump and allows fill up of tank then shut off when the float switch starts the pump again when the tank is full. Its only in my head at the moment and not sure on how to carry all this out!! Any help would be appreciated.

Jim
 
Last edited by a moderator:
not being funny but if you don't know what the N/O contact is for maybe you should get an electrician who knows what he's doing to carry out the work for you.
are you a qualified electrician?
 
I'm just asking for advice on my setup,. I haven't done much with contactors before so advice was all I was looking for Geoffa. I do know what N/O is. The question mark was to emphasize that I need help in wiring the contactor correctly and not N/O?

Jim
 
i know exactly what you want, but i cant translate it onto paper. IMO, you dont want a sol valve, they can be more hassle than they are worth. a ball cock is more than adequate. you can buy sump pumps with float switches for your pump protection.

with single phase loads on 3 pole contactors its considered good practice to use all of the poles. you do this by looping the live from t1 to l2 and then you take your outgoing feed from t2, your neutral goes straight through l3 and t3.

for the pressure switch, you may want to consider using a small relay that interupts the coil to the main contactor.
as i cannot see exactly what gear you have ect, its difficult for me to help any more, and also im crap at translating what im thinking into words that are legible to any normal man! lol
 
Thanks. The reason i'm looking at using solenoid valve is cos i'm linking more than one tank together, therefore I need the solenoid to let water in to all tanks. The float switch would only be on one tank but as they would fill at the same rate. Not sure how I go about getting them to work together As one closes, the other opens and also starting pump . Is it best practice to use a relay or can I link them in series in to the contactor. Therefore kinda making the start button obsolite. Does that make sense?

Jim
 
can you draw a small shematic of your system? the i and others may be able to suggest something. how many pumps are there? are you using multiple tanks to feed one pump? how big is your water main? ect
 
I have one 3KW vertical multistage pump with a return flow pipe to the tanks , one pressure switch on the outlet side, 5 IBC tanks linked together with 1 float switch and looking to get solenoid valve for tanks top up. The travel sprinkler I am using has a auto cut off when it has finished its run, that's where the pressure switch comes in. Thanks all for your help.

Jim
 
Consider it as three separate electrical systems. First you have a high liquid level system to control the water going into the reservoir tanks, this could be a solenoid with probes/float switch or a good old ball float valve like in a toilet. Second you have a low level safety system to stop your pump from dry running when the tanks become empty. This could also be probes and liquid level control or a float switch which interrupts the power to the contactor coil. Third you have a pressure switch or prescontrol on the discharge side of the pump to swicth it on when there's demand. Now all you need to do is figure out the best way to integrate the three systems. I'd offer a suggestion but I'm confused about the line in your OP where you say 'when the travel sprinkler comes to the end of its run.'
 
The travel sprinkler i have has a mechanical cut off valve on the sprinkler which shuts off the water flow to the sprinkler head. The pump needs to have the pressure switch as the flow from the pump to the sprinkler is still on until in reaches the desired pressure to cut out.
I did toy with the idea of ball floats but i would have to install in each tank which adds to the cost. 1 solenoid i thought might be the answer but if I go and use the ball float solution I guess it makes the system alot easier.

Jim
 
Cant you just link your tanks together below ground with a 50mm LDPE pipe and a few insert fittings? That way the tankswill find their own level and act as a single larger tank.
 
Last edited:
Here's a schematic. The two probe sets obviously have associated liquid level controllers.

Irrigation System Munga42.jpg
 
The idea of balance lines to link your tanks is a good one, but in the past weve had problems sizing this line. We found that the balance lines had to be oversized so that the last tank in the line is filing up at the same rate as the one receiving the water main.
As marvo said liquid level controllers could be used, and are relatively easy to wire. You would need one for your water make up and one for your pump protection. I can't remember the ones that we used, so I can't link to one. I don't get your pressure switch? We would need to know how your sprinkler system is set up to know that. I've used rainbird in the past, and that was straight forward.
 
I am trying to use what I have available to me with out spending to much. I have the float switch, the pressure switch,the pump , 5 ibc tanks and starter. The pressure switch is being used to protect pump, as the pressure rises after sprinkler has finished its run the pressure switch will cut in at say 8 bar. When the travel sprinkler has been set up for another run, the pressure switch will cut out and so on. It sounds a bit crude the setup. but with a solenoid valve on the water inlet I thought might be the answer? The flaw with ballcocks is the tanks will fill up constantly as the level drops where as with a sole valve they would almost empty before refill.
 
that isnt a flaw with the ball cocks, its probably their best feature. also they rarely fail.. in your idea of using a sol valve, your tanks will havwe to be sized to take the full amount of water t5hat the system will use. with a ball cock, as the water will constantly be topping up, you have more capacity.
 
I am trying to use what I have available to me with out spending to much. I have the float switch, the pressure switch,the pump , 5 ibc tanks and starter.
The sketch I gave you is just a rough schematic. You can use float switches instead of the probe system I showed and you can use 5 tanks instead of the two on the sketch. I'm not sure what 'ibc tanks' are mind you.
The pressure switch is being used to protect pump, as the pressure rises after sprinkler has finished its run the pressure switch will cut in at say 8 bar. When the travel sprinkler has been set up for another run, the pressure switch will cut out and so on.
You'll still need a small diaphragm tank to give some differential otherwise the pump will rapidly cycle on/off with even a very small leak.
It sounds a bit crude the setup. but with a solenoid valve on the water inlet I thought might be the answer? The flaw with ballcocks is the tanks will fill up constantly as the level drops where as with a sole valve they would almost empty before refill.
The fill solenoid on the sketch is controlled by the short probes in the RHS tank so refill would start after a small drop in the tank water levels. You can use a ball float valve but they tend to be more restrictive and a lot slower filling than a solenoid unless you use a larger commercial one which may well be more expensive than a solenoid. Float valves also don't always like brackish or river water, the particulates can cause problems with the seat, most half decent irrigation solenoid valves are designed to work with impure water.
 
I think ill go with ballcocks for a start. I have an old booster pump with a 24l diaphram tank so I could use that. Going on to the pressure switch and float switch, how do you guys think I should wire them in to the system? The pressure switch is 240v as is the float switch.

Jim
 
Last edited by a moderator:
The live of the supply to the pump will be via the low level float to prevent dry run and via the pressure switch normally closed contact assuming it's a 'break on rise' switch and assuming both components are AC3 rated to take the full run current. If not then use a contactor. Should be easy peasy japanesey. Does your booster pump have built-in overload protection?
 

Reply to DOL starter and switches in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi having problem with my automatic sump control board the switch, for rain water pump, is not going onto auto mode when the water level reaches...
Replies
2
Views
362
Hi I have problem wiring up DOL starter Circuit trips breaker when try to start I must be wiring something wrong Any help would be appreciated
Replies
6
Views
826
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
432
Hi Everyone, Has anyone ever encountered an undersized start capacitor (from manufacture) for a single phase pump??? I would like to integrate...
Replies
10
Views
999
I am back to try and hook up my Frankenstein compressor. 60 gal tank, Ebay 5hp motor, HF 5 HP, 145 PSI V-Style Single Stage Cast Iron Air...
Replies
0
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock