Search for tools and product advice,

Discuss DOL starting 3 Ph Motor and an RCD in the Electricians' Talk | All Countries area at ElectriciansForums.net

G

gerard

Hi,

I am having trouble with a 3 phase motor (about 1kW I think) and a tripping RCD. The motor is DOL started through a contactor and thermal overload.
Starting the motor causes the RCD to trip instantly. Is the starting of the motor causing this and would soft-starting the motor solve the problem? If so, could I just take the RCD out of the circuit?

Cheers guys
 
It's a 30mA RCD. I got the machine from another branch of our company and they told me it didn't work so i am testing it by plugging it into a 3 phase socket protected by the 30mA RCD. It's a dry clean environment - a bakery to be precise. Would you recommend putting it on circuit with no RCD or up sizing the RCD to 60mA?
 
It's a 30mA RCD. I got the machine from another branch of our company and they told me it didn't work so i am testing it by plugging it into a 3 phase socket protected by the 30mA RCD. It's a dry clean environment - a bakery to be precise. Would you recommend putting it on circuit with no RCD or up sizing the RCD to 60mA?

Er, ... i think so!!!
 
Doubtful you will get a 60mA RCD.
Why do you want an RCD in the first place.
What machine, what motor, guessing it has a motor, what motor starter/drive, what else on the machine etc.?
 
First thing you should do is PAT test the motor is seems clear you have a earth leakage somewhere, there shouldnt be a reason for a leakage on a good sound motor, what does the motor do?
 
seems like all the motor does at the moment is trip the RCD.
 
agree , paul. the correct terminology is " shove a megger up it"
 
Have you taken any IR readings? I can't understand why you've got a RCD on the drive, but never the less it shouldn't trip it. Makes you wonder why your other department gave it away?
 
Darkwood,
Sorry mate but I wholly disagree with your use of the term PAT test the motor in the post above.
LOL yes well recently got my PAT cert and a free Martindale Micropat so just zapping everything with it but yes megger will do but just done 20 motors with 3phase socket kits on so just went on my own tangent.:D
 
The machine has one DOL motor and a 1ph - 3ph inverter to drive a drum type motor. The machine is plugged into a socket in a factory and that socket is protected with an RCD. So you think there is no need for an RCD for this machine?
 
Have you taken any IR readings? I can't understand why you've got a RCD on the drive, but never the less it shouldn't trip it. Makes you wonder why your other department gave it away?
I checked the ohm readings across the motor windings as I dont have a megger. The motor is in sound condition. The reason for the RCD is because the machine is portable and can be plugged in at a few locations around the factory.
 
What inverter are you on about Paul?, O/P says its DOL with contactor and overload, makes sense now about you PAT comment which defo' wouldnt do through an inverter, hes only enquiring about whether soft starting would cure the problem.:whatchutalkingabout
 
darkwood,
In post #12 OP says the machine has an inverter, this may have leakage, if this powers up the same time as the main DOL motor it could be this taking the trip out, even if the inverter driven motor is not running the inverter may power up to ready state when the DOL motor is energised.
 
I got a machine from another branch of our company and they told me it didn't work so i am testing it by plugging it into a 3 phase socket protected by the 30mA RCD. It's a dry clean environment - a bakery to be precise. The machine is plugged into a socket in a factory and that socket is protected with an RCD. The reason for the RCD is because the machine is portable and can be plugged in at a few locations around the factory.

The machine has one DOL 3-phase motor (about 1kW I think) started through a contactor and thermal overload, and a 1ph - 3ph inverter to drive a drum type motor. Starting the DOL motor causes the RCD to trip instantly.

I checked the ohm readings across the motor windings as I dont have a megger. The motor is in sound condition.


Is the starting of the motor causing this and would soft-starting the motor solve the problem?

If so, could I just take the RCD out of the circuit?

So you think there is no need for an RCD for this machine?


Just had to rehash the tale to read it properly.

1. The motor needs an IR test to prove its integrity, as your interpretation of a 'sound' motor catches out a few skilled men!

2. I'm not too well up on 3-ph RCDs in motor circuits. I only recall RCDs working on an imbalance of currents! Have you checked for any control faults? What voltage is the control circuit?

3. Can you bench test the motor by setting up your own, non-RCD protected rig?

4. Can you try to disconnect the 1ph-3ph VFD and try the DOL?

5. A machine needs a better understanding than just plugging-in-and-hope-it-plays!

I think you'll need to offer better info, pictures, diagrams, currency to get a better ROI.

Good luck... I'm sure you'll sort it.

regs// s.f
 
Last edited by a moderator:
hi all and thanks for your help. I have a 3ph socket with a 100mA RCD and it is running fine with that. So, as someone pointed out, the 30mA RCD doesn't get on too well with the VFD. Now that this has happened, I do remember this happening before(a long time ago) and probably should have known better. thanks again.
 
darkwood,
In post #12 OP says the machine has an inverter, this may have leakage, if this powers up the same time as the main DOL motor it could be this taking the trip out, even if the inverter driven motor is not running the inverter may power up to ready state when the DOL motor is energised.
Apologies there paul missed #12 and yes all makes sense now, depending on size of inverter it would be a big suspect as 1ph to 3ph inverters create more noise than a straight 3ph to 3ph of the same size inverter, had this situe before with portable motor control rigs been plugged into 13amp sockets on different sites, im looking into a few systems to get around this fitting an earthing system monitor that cuts power if it detects a break in the earthing to reduce risk of shock as well as having adjustable rcd which will be set 30mA above natural leakage of the drive.
 
hi all and thanks for your help. I have a 3ph socket with a 100mA RCD and it is running fine with that. So, as someone pointed out, the 30mA RCD doesn't get on too well with the VFD. Now that this has happened, I do remember this happening before(a long time ago) and probably should have known better. thanks again.
Does this 100mA RCD satisfy personal safety? If the lead of this portable equipment become damaged and exposes a live conductor, does this 100mA RCD offer correct protection to the poor sod that picks up this cable and receives a new hair-do? .
 
Does this 100mA RCD satisfy personal safety? If the lead of this portable equipment become damaged and exposes a live conductor, does this 100mA RCD offer correct protection to the poor sod that picks up this cable and receives a new hair-do? .
This is a common problem with having inverters in portable equipment and really a good all round solution dosnt exist, because leakage is expected to cause nuisance tripping you have to depart from the reg's on this occasion and make it as safe as practically can be done, this includes using cable with earthed braiding and having earth circuit monitors on, the regs are not always practical in every situe but as long as counter measures are taken then youve done you bit.
 
I am going to check the regs but is a 100mA RCD not better than none?! If I make everything as safe as possible then what else can I do?
 
If the motor is not faulty then why not just take out the RCD and install a 10A triple pole type C or D mcb? This would allow for the higher starting current and provide the necessary protection needed for this type of circuit?....
 
I want to protect against leakage current and an MCB won't do this. At the moment it is protected with an MCB - still waiting for supplier to get an Si type RCD and this will solve problem - hopefully!
 
What make is the VSD as some are able to disconnect the filters that cause the tripping by a simple jumper inside the terminal cover. This is a risk based procedure based on the sites requirments for 30mA RCD prtection vs EMC issues. New Boy Ducks head and waits for flack:tounge_smile:
 
OK. Lets clarify this for the recent new posters...

The RCD is at the socket that the portable machine is plugged in to.

Gerard has the job in hand by replacing said RCD with a special type.

When he has fitted the new RCD I'm sure he'll post back here with his results.

Clear?
 
OK. Lets clarify this for the recent new posters...

The RCD is at the socket that the portable machine is plugged in to.

Gerard has the job in hand by replacing said RCD with a special type.

When he has fitted the new RCD I'm sure he'll post back here with his results.

Clear?

I sure will. As I said -I'm just waiting for part to come in, there is a delay for some reason.
 
Hi all,

I finally got the 30mA Si RCBO in today. I installed it and I'm afraid (for me!) it was bad news. It tripped instantly with the leakage current created by the Inverters. I could try an RCBO with a higher mA rating but I thought the Si range are designed for such applications. So there you go-any more suggestions on how to go about this problem?
 
OK. Lets clarify this for the recent new posters...

The RCD is at the socket that the portable machine is plugged in to.

Gerard has the job in hand by replacing said RCD with a special type.

When he has fitted the new RCD I'm sure he'll post back here with his results.

Clear?

With reply's like this Im reluctant to post here anymore. Sorry chap PM me if you like.


James
 
Hi all,

I finally got the 30mA Si RCBO in today. I installed it and I'm afraid (for me!) it was bad news. It tripped instantly with the leakage current created by the Inverters. I could try an RCBO with a higher mA rating but I thought the Si range are designed for such applications. So there you go-any more suggestions on how to go about this problem?

At what point in the cycle of the machine?
Was this immediately on power up, were the motors being driven?
 
Hi Gerard,

Any chance of posting the datasheet for the SI type RCBO ? or the part number ?

Edit: and the inverter/ vfd drive you are using ?
 
Last edited:
Hi Gerard,

Any chance of posting the datasheet for the SI type RCBO ? or the part number ?

Edit: and the inverter/ vfd drive you are using ?

I will do but not until the 27th as i am not back to work till then. I know there a two cfw 10 weg inveters driving the motors
 
With reply's like this Im reluctant to post here anymore. Sorry chap PM me if you like.


James



And your point is? :baby:



New Boy Ducks head and waits for flack
tounge_smile.gif


New Boy assumes flack, doesn't duck but makes petulant statement.
 
Last edited by a moderator:
Hi Gerard,

I managed to find the datasheets for the WEG VFD's, just when you get a chance for the RCBO's datasheet, no hurry.

Will do - thanks for that. Probably be the 27th before I get it for you. In the meantime I will scour the Schneider website - tried earlier but their site was v. slow so packed it in.
 
I will do but not until the 27th as i am not back to work till then. I know there a two cfw 10 weg inveters driving the motors

You recently stated the inverters were


Take a look at page 86, parameter P297... switching frequency. Decrease it. I have seen in IMO manuals that switching freq. contributes to RCD tripping.
 
With reply's like this Im reluctant to post here anymore. Sorry chap PM me if you like.


James

Hi James: Don't really understand what your problem is with the replies gerard has been given, especially Silva's quoted reply. gerard does'nt seem to have a problem with it, so maybe you could explain ?
 
Last edited by a moderator:
hi all

been installaing a few abb vsd's and under manufacturers info it specs that if using rcd's they must be of a B type..... 300ma td. unsure if this is the case with other drives but i would imagine that it is because of high earth leakage.

hope this is of use

regards
gary
 
hi all

been installaing a few abb vsd's and under manufacturers info it specs that if using rcd's they must be of a B type..... 300ma td. unsure if this is the case with other drives but i would imagine that it is because of high earth leakage.

hope this is of use

regards
gary

Thanks for that I will order one and give it a go - no harm in trying. I will post my results when I find out
 
No - the frequency has to remain constant for this application. Didn't try taking it out either.
As discussed previously in this section, I think the VFDs might be on the small side - this is not helping the situation either. Will try the 300mA RCD and see how it goes.....
 
No - the frequency has to remain constant for this application. Didn't try taking it out either.
As discussed previously in this section, I think the VFDs might be on the small side - this is not helping the situation either. Will try the 300mA RCD and see how it goes.....

No, not the output frequency... I said the switching frequency.

By taking out the inverter you can find if the RCD still trips, which can point to another issue, perhaps.

Is the inverter good?

Has this machine ran at all since you've had it?

.
 
No, not the output frequency... I said the switching frequency.

By taking out the inverter you can find if the RCD still trips, which can point to another issue, perhaps.

Is the inverter good?

Has this machine ran at all since you've had it?

.

I increased the ramp times to as much as I could. How do you mean take the inverters out - then nothing would happen? The inverters are good except as I said they might be a bit on the small side and at their max in terms of current capabilities. Yes, the machine is running fine with no problems except it's RCDless!
 

Reply to DOL starting 3 Ph Motor and an RCD in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
511
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock