Discuss DOL Switch Wiring in the UK Electrical Forum area at ElectriciansForums.net

Clive

-
Reaction score
0
Hi Guys

Can anyone out there help me, I’ve got a DOL Starter Switch which I want to use for my woodwork machine, but at the moment it keeps tripping out.

The switch is for a 3 phase supply 240 volt, I believe they can be wired for a single phase supply which is what I’m trying to do.

The woodwork machine is purely a hobbyist one, the plate on the motor says its 1.5HP, 1.1KW, 240V, 6.9A.

The switch I’m using is Moeller MSE-M240V Made in Germany.

As already said the switch keeps tripping out, ie if the motor is connected to the switch with no load on the motor it runs quite happily but soon as the motor is attached to a piece of machinery such as a table saw the switch trips out, if I wait about 15 seconds I can then switch the saw back on, only for it to trip again.

I’ve been told there is a connection missing on the switch which I need to make as it’s a
3 phase switch and it could be out of balance causing nuisance switching.

From my diagram could someone tell me where I need to connect the wire?

Wiring 5.jpg
 
As its drawn it won't work at all as nothing connects to A1 to pull the contactor in.

Yes you do need to balance the current through the overloads, this is normally achieved by looping the L1 output of the starter back to the L2 input, then connect the motor L to the L2 output.

Plus you need to make sure the overload is correctly set for your motor, usually set to the data plate value of running current for a DOL start.
 
Move the live to the motor from T1 to T2.

Add another connection T1 to L2

It is tripping due to unbalance


Check that once running if you operate any of the 4 interlock switches at the bottom, the motor actually stops, it isn't clear the way it's drawn that this is the case!
 
Last edited:
Check that once running if you operate any of the 4 interlock switches at the bottom, the motor actually stops, it isn't clear the way it's drawn that this is the case!

I was struggling with that too, but I think they are right.
What puzzles me is that there's no connection to A1 as far as I can see.
 
I was struggling with that too, but I think they are right.
What puzzles me is that there's no connection to A1 as far as I can see.
Yeah, I assume A1 and 13 are Interconnected, but not very clear, hence missed in the drawing, but as drawn, yup an issue.

Not fully sure about the safety circuit, I sort of think it's right, but think it ought to be checked.
 
Yeah, I assume A1 and 13 are Interconnected, but not very clear, hence missed in the drawing, but as drawn, yup an issue.

Not fully sure about the safety circuit, I sort of think it's right, but think it ought to be checked.

They are in series with the hold in contact and overload N/C so should work.

But yes every safety device should always be checked regardless.
 
Agree with all you two say. It's pretty common knowledge to use two of the main contacts in series for the live supply but not surprisingly uncommon for non industrial sparks or learners. It wants looking into with the coil connection, as you say.
 
As its drawn it won't work at all as nothing connects to A1 to pull the contactor in.

Yes you do need to balance the current through the overloads, this is normally achieved by looping the L1 output of the starter back to the L2 input, then connect the motor L to the L2 output.

Plus you need to make sure the overload is correctly set for your motor, usually set to the data plate value of running current for a DOL start.


Hello Davesparks

Thank you for your reply, when you say it won’t work at all as nothing is connected to A1 to pull the contactor in, the motor does run as per my diagram but it keeps tripping out once a load is applied.

As far as the overload is concerned, I’ve got it set at the maximum which is 6 amps see my attached picture.

I understand I might be out of luck and need a higher overload rating but I wanted to make sure I’d at least got it wired up correctly first.

Obviously if it’s still tripping after that I assume it’s got to be the overload rating in which case I’ll have to buy another switch but I will go for a single phase one next time.
Overload Setting.JPG


Spec Plate.JPG
 
Move the live to the motor from T1 to T2.

Add another connection T1 to L2

It is tripping due to unbalance


Check that once running if you operate any of the 4 interlock switches at the bottom, the motor actually stops, it isn't clear the way it's drawn that this is the case!


Julie

Have a look at the updated diagram, can you confirm that is what you mean, thank you.

Wiring7.jpg

[automerge]1585603955[/automerge]
There must be something connected to A1 to make it work. Would it be possible for you post a picture of the top half of the contactor.


Hi Dave

The only diagram of the switch is inside the cover see attachm
P1010058.JPG
ent, but I will take some more pics tomorrow.
 

Attachments

  • Wiring 6.jpg
    63.2 KB · Views: 3
Last edited:
Looks like you have 4 remote N/O 'start' buttons, closed, in series in your drawing. They should be stop buttons, breaking the circuit on push, if the wiring is correct. The start/stop involves the overload mechanism. That on the cover shows 2 start contacts, one remote, linking 13 and 14 and then on to A1, the link missing on your drawing. Your drawing isn't correct, so, if it operates, it's not wired as you indicate. Various things need addressing. Are those four all stop buttons, for example?
 
Hello Davesparks

Thank you for your reply, when you say it won’t work at all as nothing is connected to A1 to pull the contactor in, the motor does run as per my diagram but it keeps tripping out once a load is applied.

As far as the overload is concerned, I’ve got it set at the maximum which is 6 amps see my attached picture.

I understand I might be out of luck and need a higher overload rating but I wanted to make sure I’d at least got it wired up correctly first.

Obviously if it’s still tripping after that I assume it’s got to be the overload rating in which case I’ll have to buy another switch but I will go for a single phase one next time.
View attachment 56769

View attachment 56770

The overload is incorrect for that motor, the data plate clearly gives a running current of 6.9A but the overload has a maximum setting of 6A.

I don't think single phase DOL starters exist, you just adapt a three phase one to suit.
 
ipf
There’s nothing like cocking something up, my apologies for getting the diagram wrong please see the revised Wiring Diagram 7 the four emergency stop buttons are all normally closed and if one of them is pressed it has to be locked back on and the machine can only be restarted by pressing the DOL Starter button.
Wiring Diagram 7.jpg

[automerge]1585663985[/automerge]
Davesparks

David Prosser is correct there is such an animal as single phase DOL Starters, in fact with the help of you guys in may very well turn out to be a case of the 6A overload on the one I’ve got just won’t hack it.

I’m assuming the 6.9 amps rating on the motor plate is the maximum as it does not say.

I suppose I could buy a clamp on ammeter and check the current draw.
[automerge]1585664537[/automerge]
Guys

Will you all please take a look at the revised Wiring Diagram 7, sorry for getting the original one wrong.

The e/stops are all N/C, plus there is a link between terminals 13 NO and A1.

Can someone confirm if Wiring Diagram 7 is correct for also balancing the phases??
If it is still wrong I'd really appreciate it if someone could modify Wiring Diagram 7 and post it on here.

If it is, I will change how the starter is wired at present and see if it still trips out, if it does then I will have to buy another starter with a bigger overload current setting.

Iv'e also included a few pics of the starter.



Wiring Diagram 7.jpg


P1010087.JPG


P1010090.JPG


P1010094.JPG


P1010098.JPG


P1010101.JPG
 
Last edited:
ipf
There’s nothing like cocking something up, my apologies for getting the diagram wrong please see the revised Wiring Diagram 7 the four emergency stop buttons are all normally closed and if one of them is pressed it has to be locked back on and the machine can only be restarted by pressing the DOL Starter button.View attachment 56794
[automerge]1585663985[/automerge]
Davesparks

David Prosser is correct there is such an animal as single phase DOL Starters, in fact with the help of you guys in may very well turn out to be a case of the 6A overload on the one I’ve got just won’t hack it.

I’m assuming the 6.9 amps rating on the motor plate is the maximum as it does not say.

I suppose I could buy a clamp on ammeter and check the current draw.
[automerge]1585664537[/automerge]
Guys

Will you all please take a look at the revised Wiring Diagram 7, sorry for getting the original one wrong.

The e/stops are all N/C, plus there is a link between terminals 13 NO and A1.

Can someone confirm if Wiring Diagram 7 is correct for also balancing the phases??
If it is still wrong I'd really appreciate it if someone could modify Wiring Diagram 7 and post it on here.

If it is, I will change how the starter is wired at present and see if it still trips out, if it does then I will have to buy another starter with a bigger overload current setting.

Iv'e also included a few pics of the starter.



View attachment 56796

View attachment 56797

View attachment 56798

View attachment 56799

View attachment 56800

View attachment 56801

It looks OK to me.

The point is to make sure all the safety interlocks/switches work physically.

As for the overload - motor rating, the current draw on a motor is very dependent upon the load applied. So if you are running the machine for long periods with no load at all the current is likely much less than 1.5A, under moderate load say 5A, and so on - the point being is that if you do run it at the maximum it can safely take then you would need a new overload to do 6.9A but, if it's not running at this for any length of time a lower rating (6A) would suffice.

The only issue would be that if it's started and stopped frequently and run close to maximum, then the overload could trip.

Given that you have everything in place other than the L2-T1 link, I would just add it and make sure everything is OK - it's likely to be absolutely fine.

If you do need to change the overload, I would just change the overload, not the full unit - it's a standard part.

The single phase DOL starters are exactly the same as the one you have - they just already have a link L2-T1!
 
Julie

iv'e just got around to trying the machine again,, its fine when motor is running but as soon as I push a piece of wood through saw it stops, so it does look as though the overload won't hack it.
[automerge]1585755565[/automerge]
David Prosser
Thanks for the
 
Julie

iv'e just got around to trying the machine again,, its fine when motor is running but as soon as I push a piece of wood through saw it stops, so it does look as though the overload won't hack it.
[automerge]1585755565[/automerge]
David Prosser
Thanks for the

Stops as in stalls the motor, or trips the Overload?

If it's the motor stalling , that won't be the overload - it would be something else.

If it is just tripping the overload under load - then a new one is needed!
 

Reply to DOL Switch Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
340
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
574
Looking for counsel / guidance to replace an original Dayton On/off with speed control switch. I’ve checked with a couple local electrical supply...
Replies
5
Views
705
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
947
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
476

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock