I'm not sure BS 6004 6242y twin and Earth is specified as domestic cable. But you definitely would usually expect to see it more in domestic settings.
Just like the low smoke version BS 7211 6242b you would usally expect to see more in a public building or commercial type setting.

Both are recognised in the BS7671 as technically better than YY SY cable that are non standard.
 
Last edited:
We have stock of big sizes of twin and earth up to 25mm sq. From memory it's a single solid conductor up to 16mm sq, after that it has multistranded conductors sao maybe the solid conductor sizes are classed as domestic and the larger multistranded sizes are commercial. I think it might actually be available in sizes even larger than 25mm sq as well.

If the motors are run by inverters or drives or any kind of high frequency modulated supply you should avoid using solid conductor cables.

One limitation with twin and earth can be achieving disconnect times with the undersized CPC. Maybe that's why they class it as a domestic cable in the UK because with longer runs and higher potential fault currents in commercial installations it would certainly be a limiting factor.
 
I would like to know out of curiosity, westward10 - is that unheard of? Might be useful information in the future you never know.

And i’m not sure, just didn’t seem like it was good practice for some reason in my head. Can’t put a finger on it.
 
Each motor unit can be switched on and isolated by the rotary isolator adjacent to it.

Units are connected to the isolators by T&E cable as well.

No solid answers so far as to why it would be a bad idea to use twin and earth other than the install not looking as good as it maybe could have done.
 
Disconnection times referring to the undersized CPC in T +E.
Vibration issues in terminations of the final length Rotary to Motor control are the answers picked up from the responses so far.
A J - disconnect times
Marvo - undersized CPC
Everyone else - vibration issue
 
Disconnection times referring to the undersized CPC in T +E.
Vibration issues in terminations of the final length Rotary to Motor control are the answers picked up from the responses so far.
A J - disconnect times
Marvo - undersized CPC
Everyone else - vibration issue
With regards to Vibration issues, I was one of those who supported that, but what about MICC that had solid core conductors, although Electricians sometimeput a loop in the cable to counter act vibration.
 
No problem with disconnection times and the earths all seem suitably sized. 6mm twin and earth is the largest in place. There has been 2 x 10mm SY cables installed as well where the earth is obviously the same size as the line conductor.

Regarding the vibration issue, unless I’m missing something or not thinking fully, what difference would a stranded core cable make to a solid core cable if both had a nice tight connection? Or is it not the cable coming loose which you are getting at?

Thanks.
 
The name flexible cable will be the clue here, seeing as the motors will be vibrating a solid core cable is more liable to snap in the termination than a flexible one.
 
Excuse me if I’m being ignorant but what makes you think a solid core cable will snap with a bit of vibration unless the copper had been nicked or damaged?
Something that is of solid construction, is more prone to breakages than something that is flexible, especially solid conductors.
 

Reply to “Domestic” Cable for Motor Applications in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
635
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
593
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Evening all. Been at a property the last couple of days that had suffered damage due to a surge. I got the power back on all circuits apart from...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock