There are thousands of installs like this with no single point of isolation,usually a number of isolators from a henly block. All it needs is a label stating that all isolators need to be off in order to isolate the entire installation. It's a code 3 for me,I cant see a potential danger unless standard safe isolation proceedures are not followed,which is not something which can be reasonably allowed for.
I see that method used all the time. 6mm taken off the tails on mains side of switch. It's very common practice. Rough as!
Yes agree code 3 for no single point of isolation but code 2 for no RCD on shower thinks
2005?
I only did my 2330 in 2011 so I'm not clued up on previous versions of 7671
And when is it you think I said this?So, every non RCD'd circuit in a domestic installation in a code 2, then, is it?
So, every non RCD'd circuit in a domestic installation in a code 2, then, is it?
Dont think Amckay is implying that,although I do think there is a tendency amongst the more recently qualified to panic at anything not on an RCD.
Yes agree code 3 for no single point of isolation but code 2 for no RCD on shower thinks
Why? Code 3 surely.
I used to go with the code 3 observation for no RCD for a showers but was pulled up by my scam that it should be a code 2 . If there was supplementary bonding I would Code 3 it though , and as stated its the circuits not the appliance that as to be protected any way , I think its a tuff one to call and would no argue with the code 3 if on a report done by others,but would go for a code 2 in most situations if I was doing the test unless you can convince me otherwise.
Well, yes but that's a different matter, isn't it?They said that if there was earth leakage and no supplementary bonding and you are soaking wet in the shower then the risk of electric shock is higher and use of an RCD would give you the additional protection.
The regs. are rarely retrospective so 'improvement recommended'.I feel that just because it a new regulation and was not in the 16th it not necessary just a deviation from the regulations and code 3 it ,it down to each installation for example maybe a care home full of venerable people or a rented accommodation where the tenant will use any excuse to say the electrics are unsafe An RCD would be a good idea, were do we draw the line as regs get updated,
We test to the current regs. and bear in mind the regs at the time of installation.I know we test the installation to the regs at the time
Even safer now does not mean it was dangerous.it was installed but surely the regs are updated to improve the safety of the installation and just giving all new reg deviations a code 3 does not seem right.
A profound statementWell, yes but that's a different matter, isn't it?
Without RCD protection at the time there should have been supplementary bonding so a code 2 would be for the lack of bonding, not lack of RCD.
The regs. are rarely retrospective so 'improvement recommended'.
We test to the current regs. and bear in mind the regs at the time of installation.
If it was considered 'safe' at the time it cannot be potentially dangerous now - so improvement recommended.
Even safer now does not mean it was dangerous.
An old car without seat belts is less safe but is it potentially dangerous?
The car itself will be less safe but is it potentially dangerous?