Hi folks,

Friend is currently renovating his house, including a loft conversion. He had originally hoped to go with Grade F1 (tamper proof batteries) radio interlinked alarms. However architect has stipulated all alarms must be Grade D (mains powered with battery back-up), but can be still be radio interlinked.

All walls and celling's are up, plastered and painted. So looking to minimise damage where possible when installing.

It's going to be pain to run a separate circuit from CU for alarms and to have them hardwired interlinked, but if needs to be done that way then so be it. Same would also apply if running separate mains alarm feed cable connecting into lighting circuit MCB at CU.

So was wondering what your views would be on doing the following (not ideal in my mind, but a possible workaround).

  • Downstairs alarms mains feed of downstairs lighting circuit (can 'easily' access - minimal damage).
  • Upstairs alarms mains feed of upstairs lighting circuit (can 'easily' access - minimal damage).
  • All alarms radio interlinked (could hardwire interlink downstairs, hardwire interlink upstairs with radio interlink between upstairs and downstairs).

Look forward to your input.
 
No rules stipulating that they have to be on the same circuit.

Also the Scottish government standard allows for radio Interconnected systems.

Just check that the alarms, type, location, and quantity complies with the tolerable standard as issued by the Scottish government.

Btw there is no regulation in the Scottish standard that prohibits the use of fixed battery alarms Interconnected via radio.

Did the architect misunderstand what was being suggested?
 
The only risk that I see you might have to be careful to avoid the possibility of shared or borrowed neutral .

Hard wire interlinking is often done with a live feed from one to the other, if they are on separate circuits then some current will pass down wrong neutrual.
 
No rules stipulating that they have to be on the same circuit.

Also the Scottish government standard allows for radio Interconnected systems.

Just check that the alarms, type, location, and quantity complies with the tolerable standard as issued by the Scottish government.

Btw there is no regulation in the Scottish standard that prohibits the use of fixed battery alarms Interconnected via radio.

Did the architect misunderstand what was being suggested?
Thanks for input. Separate circuits will save a lot of work. :)

All I know is that my friend has been back and forward with the architect over this, and architect is refusing to budge on this, so to keep the peace will be going with Grade D alarms as stipulated by the architect, hence OP.
[automerge]1592820722[/automerge]
The only risk that I see you might have to be careful to avoid the possibility of shared or borrowed neutral .

Hard wire interlinking is often done with a live feed from one to the other, if they are on separate circuits then some current will pass down wrong neutrual.
Interlink between downstairs and upstairs circuits would be radio not hardwired, so no risk of borrowed neutrals. Thanks.
 
D2, LD2 which means mains powered as per BS5839-6. As suggested you could radio link them.

Btw there is no regulation in the Scottish standard that prohibits the use of fixed battery alarms Interconnected via radio.
But BS5839-6 Table 1 does prohibit this?
 
D2, LD2 which means mains powered as per BS5839-6. As suggested you could radio link them.


But BS5839-6 Table 1 does prohibit this?
Would appear BS and Scottish government are not 100% in sync.

Guess Scottish government position is that having smoke alarm(s) whether it's mains or battery powered is better than not having any at all.

On a separate note, if I bought every BS standard that I would touch upon, then storage of these alone (forest of paper) would results in an increased fire risk ;)
 
D2, LD2 which means mains powered as per BS5839-6. As suggested you could radio link them.


But BS5839-6 Table 1 does prohibit this?

Not on existing properties - F2 would be acceptable - but NOT in Scotland, here F1 is the minimum, it depends on how upgraded the property is, but if it's a loft conversion then the loft portion may be regarded as materially altered so D2 there.
 

Reply to Domestic heat/smoke alarm mains powered from different lighting circuits? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
261
Hi Folks.....I'm replacing hard wired interlinked smoke alarms with new battery interlinked ones. I disconnected old alarms and left the wires...
Replies
6
Views
1K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
Hello all. I have visited a domestic property with two consumer units, one downstairs and then a separate one for upstairs. The upstairs is fed by...
Replies
3
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock