I'm currently producing a business plan and I need some figures and time scales......

According to GN3 all domestic premises should be Inspected and Tested every 10 years. So when is an installation likely to be issued with a rewire due to deterioration of cables etc. I know it is impossible to say but can we put a ball park figure on this?
 
There's no reason why a good installation with modern PVC cables shouldn't have an expected life of over 100 years. Within this time one would expect to replace accessories.

The main cause of deterioration of cables (other than damage due to poor installation or during service) is the thermal cycling as loads vary. In domestic, cables aren't generally subject to environmental stress.
So, if a house only has one sockets and one lights circuit, the cables may only last 50 years. With more circuits lightening the load on the cables (and now the use of low energy lighting) the cables will see less thermal cycling and so their life will be considerably extended.

As with all things however, there are many individual factors which will contribute to the expected lifetime.
 
Well PVC was supposed to last the life of the building, however some of the earlier PVC suffered from the dread 'Green Goo' reaction.
I would say the most likely cause of needing a rewire is - Lack of sockets, Lack of circuits and lots of alterations.

In general any pvc I have tested on IR etc. has not detiorated. This includes singles from the 60's etc which are now 50 years old and in heavyish daily use.
 

Reply to Domestic Rewires - When in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
587
Why are cctv installers in ireland not using LSHF cable in a domestic situation as when wiring Sockets/ LIGHTS rtc Irish regs state thst LSHF...
Replies
14
Views
3K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
HI I am thinking of using steel cable tray or or basket with a cover for a vertical in a domestic garage to the consumer unit. I am looking at...
Replies
14
Views
5K
Hi Guys I am 19 years old and currently an automation maintenance engineer (3 year BTEC/NVQ LVL3 apprenticeship) at a large industrial firm and...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock