Discuss Double pole mcb poles in the UK Electrical Forum area at ElectriciansForums.net

Mikegh

Esteemed
Reaction score
695
I've a C63 10kA DP MCB

Is there usually protection on both poles or is 1 pole a switch?. I'm not seeing any markings to indicate either way. Cheers.
 
A double pole circuit breaker is essentially 2 circuit breakers put together. If one trips then the other will.
 
Double pole MCB is just that - two identical MCBs joined together. I live in an area where split or two phase 460 volt supplies are common, so they have been a stock item for me.
Not to be confused with single pole plus neutral devices, which are generally available as RCBOs rather than MCBs. The neutral on these is just a switch.
 
Is it a single module or a double width module?
If it is double width, so 2 MCB's attached to each other, it will almost certainly be double pole.

If it is a single module width then it may be a double pole MCB or it may be a single pole switched neutral MCB. Check the functional diagram on it if it has one, or else check the part number against the manufacturers data sheet.

You can always post a picture here and we someone will probably be able to tell.

SPSN rcbos are starting to become more common but unfortunately are often being described incorrectly as DP, I'm not sure if the same is true for MCB's.
 

Reply to Double pole mcb poles in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
855
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
603
I need to replace a Hagar RCD (model number CN284U). This is a type AC RCD and I wish to replace it with a type A. The model number for the Type...
Replies
28
Views
4K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
901
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock