Search the forum,

Discuss Downlighter max amount on one circuit. in the Australia area at ElectriciansForums.net

B

Bigboy247

Was looking a a job today in a kitchen, the customer had 12 gu10 50w 240v mains downlighters off one switch, 6amp mcb to 1.5cm T&E. Then had a thought ,yes it does happen?

12 lights x 50watts = 600
______ = 2.608 amps
230 v
She has asked for 12 more gu10 50w 240v which will take it to 1200w /230v = 5.217amps all fine but on the same circuit 4 100amp ceiling roses which takes it to 1600w ,so 6.956 amp so greater that the fuse.Yes can use diversity so below 6 amp but should I recommend some light get down rated.Hope I got my maths right as been a long time since school.But she then asked about all 24 lights on one switch where she has 2gang it the moment ,would this trip the mcb due to sudden inrush when the switch opens to 24 gu10.She will not have Elv 12v ones as the transformers can never be replaced or hidden due to the nature of the customers requests.Yes I know its special location.
 
What about the low energy fluorescent type gu10's? think there about 13w, obviously a different concentration of light compared to halogens but it would reduce the demand considerably
 
I have asked the customer about other lighting options but will only have 50w GU10 as she requires the room to be as bright as possible and only wants very bright downlighters and she has tried samples of the alternatives and love them or hate them the customer knows what she wants.I got some top end LEDs and they still not good enough.
 
Pop a 10A MCB in the CU (or RCBO if not RCD protected), at the end of the day as a max you could get away with a 16A (not ideal) on 1.5T+E if installation methods ok!

Problem solved, no stress!
 
Last edited:
Hi,
why not 6 amp C type mcb ? That should be ok with the sudden surge upon switching on, or an alternative 10 amp B type.

Sav
 
I'd go to a B10A. There shouldn't be a peak above that as the lamps have a resistive load rather than an inductive load. i think that's right. I know what I mean.!£$&*&^. Bl*&dy red wine again!!
 
think yourself lucky she hasn't asked you to put them all on a dimmer switch!
 
God forbid, house is like a bomb site after a bad fire and they have a thousand and one ideas, I will have to post some pictures on here as the kitchen fitters ripped out the kitchen with all the sockets off and just the wires sticking out the back boxes still live. Cooker switch is now inside the wall how they managed so much damage to the kitchen I will never know. Lights supply was just cut through left live hanging down (live), not good when your 6"3 and theres no celing only live cables as they have kids took two hours just to make safe H&S /trading standards coming tomorrow so no more kitchen fitters I will see young sky walker. I still can`t believe people can walk away and leave it like that,was a favour for there friend who phoned me and as good will went round after work and was horrified.
 
Well sure I have both in the van for emergency purposes.But its all money at the end of the day and the way the climate is at the moment no one can turn down work.
 

Reply to Downlighter max amount on one circuit. in the Australia area at ElectriciansForums.net

Similar Threads

Hi, asking for a friend in Australia. She wants to install two Pendant lights over a kitchen island and four downlights all on the same switch...
Replies
1
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
801
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Evening All, Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board...
Replies
4
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock