Hello guys/girls,
I am no electrician nor do i claim to know anything other than what i read or am told, hence why I'm here asking for your help. I have in the past added plug sockets coming off a spur, and that's about it. My goal is to replica my single light in the kitchen to 8 downlights. Ideally i would get an electrician in to do it, but i just can't afford it. So the plan now is to do all the labour and wire it up myself (with your help ;) ) and before its connected get a qualified electrician to certify it.
I have spent the last few days trying to get some information on how to wire it up and all the other things needed to make sure it's done correctly. I know about leaving enough space because of heat issues but my main concern is the wiring. Can you correct me or just confirm that what i plan to do is correct before the electrician comes and checks?
The downlights are 240v mains lights gu10, with 50W GU10 Halogen bulb, at the moment there is only 1 light in the kitchen, i have got 1.5mm twin and earth cable, is that the right wire? The information i have obtained from various web sites it that a "daisy chain" set up is best but surely it cant be as easy as wiring up from the 1st light to the last light one after the other? or would a junction box be better? Last question and i know I'm probably going to make myself look a bit daft but i just need this to be confirmed. To get the "daisy chain" wired up do you wire the 1st light from the mains (the wire that is feeding the current light) and use the same live and neutral sockets of the 1st light to feed the 2nd light with the twin and earth wire i bought? so essentially each light will have 2 wires in the live and neutral socket, a feed in and out, or am i way off the mark?
like i said i am going to get a sparky to check it all out before it goes live and just want to do the work my self to keep the cost down.
Any help would be much appreciated. thanks
 
You need to rethink your approach.

Are you energy concious AT ALL? How many icebergs will you personally melt by replacing a perfectly adequate single lamps (60watts, perhaps) with 400watts of torch lights.
They are called DOWNlights for a reason, you know.

You'll then notice that you cannot see anything on the work surfaces so you'll need to be adding more lights under the cupboards so you can see to spoon the caviar onto the blinis...and another over the sink so you can see the greasy plates properly.

Oh and as a PS

re
the plan now is to do all the labour and wire it up myself (with your help ;) ) and before its connected get a qualified electrician to certify it.

That is not how it happens. Electricians can only notify work that they have done themselves. Electrical work in a kitchen is notifiable.
If you are competent and have the right test gear you can do it yourself and pay the local authority a fee of around ÂŁ200 plus another fee for their electrician to check it all out. From your post i would suggest this is not your best option.

Or you can have a registered electrician do the work, certify and notify it. Please take that route.


 
Why not wire it as you feel necessary then when the spark comes to test it he tells you what needs changing etc. Seems like you want to screw over a friendly forum and just pay someone the bare minimum.

Either dig deep or at least dont try and take us for idiots.
 
Easy to make a real pigs ear of downlights mate, and although this may seem unhelpful, It would be better saving up a bit and getting an electrician to fit, the fitting can burn really hot (if halogen lamp)and really need to be fitted correctly and terminated well using heat resistant flex.
 
You don't tell us how your original light is wired, I think this will be another problem when you get to it.
you best bet, and also save you money, if you wish to go up that route, is to get an electrician in for you, tell him you will cut the holes in the ceiling (ready for him coming) and have the carpets & floorboards up ready for him arriving (if req'd)
This will save you money and you will know its done right AND SAFE

I would also look into using LED bulbs also, the bulbs will cost more, but will pay for themselves over and over
 
Your right in what you say in the wiring and i feel sure you can do this but please switch of at the Main and let everyone else in the house know you have done this. Pro electricians lock out the fuse box so someone dont come along and switch it back on whilst your hanging from the live. Your 1.5 twin and earth is fine but you should consider going down the low energy route if you can afford it. Be careful whilst drilling the holes for the downlights as to not catch existing cables etc. Take it slow and think it through and you should be OK........BTW ignore the silly comments that your going to get from certain memebers that think you need an electrician to change a fuse. But if you feel your getting out of your depth dont hesitate to call in a pro.
Hello guys/girls,
I am no electrician nor do i claim to know anything other than what i read or am told, hence why I'm here asking for your help. I have in the past added plug sockets coming off a spur, and that's about it. My goal is to replica my single light in the kitchen to 8 downlights. Ideally i would get an electrician in to do it, but i just can't afford it. So the plan now is to do all the labour and wire it up myself (with your help ;) ) and before its connected get a qualified electrician to certify it.
I have spent the last few days trying to get some information on how to wire it up and all the other things needed to make sure it's done correctly. I know about leaving enough space because of heat issues but my main concern is the wiring. Can you correct me or just confirm that what i plan to do is correct before the electrician comes and checks?
The downlights are 240v mains lights gu10, with 50W GU10 Halogen bulb, at the moment there is only 1 light in the kitchen, i have got 1.5mm twin and earth cable, is that the right wire? The information i have obtained from various web sites it that a "daisy chain" set up is best but surely it cant be as easy as wiring up from the 1st light to the last light one after the other? or would a junction box be better? Last question and i know I'm probably going to make myself look a bit daft but i just need this to be confirmed. To get the "daisy chain" wired up do you wire the 1st light from the mains (the wire that is feeding the current light) and use the same live and neutral sockets of the 1st light to feed the 2nd light with the twin and earth wire i bought? so essentially each light will have 2 wires in the live and neutral socket, a feed in and out, or am i way off the mark?
like i said i am going to get a sparky to check it all out before it goes live and just want to do the work my self to keep the cost down.
Any help would be much appreciated. thanks
 
Your right in what you say in the wiring and i feel sure you can do this but please switch of at the Main and let everyone else in the house know you have done this. Pro electricians lock out the fuse box so someone dont come along and switch it back on whilst your hanging from the live. Your 1.5 twin and earth is fine but you should consider going down the low energy route if you can afford it. Be careful whilst drilling the holes for the downlights as to not catch existing cables etc. Take it slow and think it through and you should be OK........BTW ignore the silly comments that your going to get from certain memebers that think you need an electrician to change a fuse. But if you feel your getting out of your depth dont hesitate to call in a pro.

So bonding, RCd protection, load on circuit are already fine are they?
 
Some of us joined the forum to offer help to people, not just to slag every person asking for help off. It does the proffesion or the forum no good whatsoever. I suppose you go to the garage to get everything done on your car !!! The OP has had the sense to ask for advice. 1000's of people out there would haver just gone to BnQ and wacked the downlights up without a thought.
So bonding, RCd protection, load on circuit are already fine are they?
 
No far from it, but to do jobs correctly. All I pointed out was what needs to be in place in regards to altering a installation. Advice should be the correct advice and not just what someone wants too hear.

All work has to comply with the current version of BS7671. Which states all what i have said shoul;d be satisfactory before carrying out the works asked about.
 
best way. find out where you can fit the downlights, avoiding joists.cut the holes the correct size. get the floor up above. daisy chain your 1.5mm from the existing light to the 1st downlight, then 2nd, and so on. then call in a spark to correctly wire them, test them, check your earthing and bonding etc.
 
Spot on Tel great advice m8.
best way. find out where you can fit the downlights, avoiding joists.cut the holes the correct size. get the floor up above. daisy chain your 1.5mm from the existing light to the 1st downlight, then 2nd, and so on. then call in a spark to correctly wire them, test them, check your earthing and bonding etc.
 
Some of us joined the forum to offer help to people, not just to slag every person asking for help off. It does the proffesion or the forum no good whatsoever. I suppose you go to the garage to get everything done on your car !!! The OP has had the sense to ask for advice. 1000's of people out there would haver just gone to BnQ and wacked the downlights up without a thought.

I don't no, but at the same time I don't have to go onto mechanics forums asking how to do the work, when I really haven't a clue.

My stand on topics like this is that if you need to ask a question regards a little part of the work then fine, but if you basically ask how its done from the first to the last step, then this to me demonstrates that the person asking has no idea at all what he or she is doing and IMO should leave it to some one who does.
 
Thanks mayfair and telectrix for your input and dillb if you cant be arsed to help or advise in a way where u don't sound like a sarcastic dick then don't bother. Like i said before i don't know 100% how to do it hence why i asked for help from people that do and if i am close to getting it right and some one can help me then great, but if i'm a million miles away, then i can do as much as i can before i call the pro's in.
just a note for the people that are willing to help, i'll be placing the lights from above by lifting the carpets and floor boards to make sure no pipes/wires are touched and the joist won't be drilled. Tele your exactly right in the approach, nothing will be completed until a pro sparky has checked everything and said its fine.
I'll definatly reconsider the bulbs.
 
Has anybody mentioned fire hoods yet?

If you're not going to spend out on a professional at least opt for decent fittings and lamps that won't burn your house down. I suggest JCC Led 7s or if you want swivelly ones any fire rated unit + GE, kosnic, LEDlight etc lamps
 
Thanks mayfair and telectrix for your input and dillb if you cant be arsed to help or advise in a way where u don't sound like a sarcastic dick then don't bother. Like i said before i don't know 100% how to do it hence why i asked for help from people that do and if i am close to getting it right and some one can help me then great, but if i'm a million miles away, then i can do as much as i can before i call the pro's in.
just a note for the people that are willing to help, i'll be placing the lights from above by lifting the carpets and floor boards to make sure no pipes/wires are touched and the joist won't be drilled. Tele your exactly right in the approach, nothing will be completed until a pro sparky has checked everything and said its fine.
I'll definatly reconsider the bulbs.

Same old story:nopity:
 
DIY Bob as you put it must get fed up of visiting for advice and getting abuse from some forum members that think wiring downlighters is some sort of secret work that can only be achieved by studying for 5 years. IMO
 

Reply to downlights intallation help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
895
I am installing 9 LED downlights each with an RGB bulb in (i will try attach pictures on them) - anyway I have been told that they need to be...
Replies
4
Views
758
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
440
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
515
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock