Reaction score
41
I have installed a 16a 3 phase extract fan, when doing my testing after id finished i had 403v between phases, boss thinks this is ok but i think its a bit low, anyone?
 
If it's consistently between all phases then as Lenny says it's fine. If for some reason you were getting a wide variance between two of the phases it would be a cause for more head scratching.
 
What is the voltage at the origin of the installation? from this you can determine the voltage drop and wether it is acceptable or not i.e. does it exceed 5%.
it would need to be 424 V at the origin or more to exceed 5% on the voltage you have given. Another deciding factor is what the manufacturers instructions say is the minimum limit.
 
Seems i may have grabbed the wrong end of the stick and ran with it fir all it was worth.

Are you saying your 403V was measured at the 'load' end of your new circuit, under load???
 
the problem lies in the use of cable already present, its a 2.5mm multi core 10 with 5 cores being used, IR was sound >299 , just money saving by the boss
 

Reply to Drop over 3 phases in the Australia area at ElectriciansForums.net

Similar Threads

Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
431
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
936
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock