Discuss Drop over 3 phases in the Australia area at ElectriciansForums.net

Reaction score
41
I have installed a 16a 3 phase extract fan, when doing my testing after id finished i had 403v between phases, boss thinks this is ok but i think its a bit low, anyone?
 
If it's consistently between all phases then as Lenny says it's fine. If for some reason you were getting a wide variance between two of the phases it would be a cause for more head scratching.
 
What is the voltage at the origin of the installation? from this you can determine the voltage drop and wether it is acceptable or not i.e. does it exceed 5%.
it would need to be 424 V at the origin or more to exceed 5% on the voltage you have given. Another deciding factor is what the manufacturers instructions say is the minimum limit.
 
Seems i may have grabbed the wrong end of the stick and ran with it fir all it was worth.

Are you saying your 403V was measured at the 'load' end of your new circuit, under load???
 
the problem lies in the use of cable already present, its a 2.5mm multi core 10 with 5 cores being used, IR was sound >299 , just money saving by the boss
 

Reply to Drop over 3 phases in the Australia area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
360
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
658
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
789
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock