davidjones89

if someone can clear this up please, when upgrading a CU to comply with the current regulations, does the new unit have to be a dual RCD to avoid tripping off the entire installation in the event of a fault or is it still acceptable to have just an RCD board :confused:
 
Hi davidjones,

I remember that this is in the building regs somewhere, downstairs ring and upstairs lights and vice versa
on seperate RCDs. 671 doesn't tell much about that. It might be in part M of the BR?
I'm sure I read it in this forum somewhere some time ago ...
 
If you go to any wholesaler or even B&Q and purchase a "17th edition board" they'll come with two RCD's as standard. To completely and utterly comply with regs, in an ideal world, each circuit would be on its own RCBO, but this can be costly.
 
Ol' red says something like "circuits should be installed so as to minimise inconvenience in the event of a fault"

So technically a single RCD board would contravene the regs as all circuits would be lost in the event of a fault........properly inconvenient.:)

As the lads have said either a dual RCD board with up and down lights and sockets shared over the two, or a main switch board with individual RCBO's for each circuit (mucho expensivo).:D
 

Reply to Dual RCD CU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
661
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
773
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock