    Fitted a new outside light for customer and dusk to dawn lamp, the lamp keeps flashing off and on every 20 seconds.
    Found the fault to be the reflection from the clear plastic housing is lighting up the photocell and causing the lamp to switch off, then in darkness the lamp switches on again.
    The only solution I can thin off is either a miniature photocell I can hide somewhere or a timer that is a direct replacement for a light switch that will be compatible with LED lights.
    Neither of which I can find.

    Any other suggestions.


    Thanks.
     
  2. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Have you put a LED lamp in or is the fitting itself LED?
     
  3. Rappid
    Offline

    Rappid Electrician's Arms

    Location:
    Wickford, Essex
    It's a LED lamp with built in photocell
     
  4. haptism
    Offline

    haptism Regular EF Member

    Location:
    SW. London
    Some of those type of lamps flash on/off a few times to acknowledge what setting its on. Not sure about every 20 seconds thou; is there nothing listed in the instruction book.
     
  5. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
  6. Rappid
    Offline

    Rappid Electrician's Arms

    Location:
    Wickford, Essex
  7. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    Is the sensor built in, if so where isit positioned, could you upload a photo? If the light output of the fitting is untriggering the photocell then the photocell sensor will need reloacting.
     
  8. Rappid
    Offline

    Rappid Electrician's Arms

    Location:
    Wickford, Essex
  9. Andy78
    Online

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    If the fault is the combination of the lamp and the fitting itself then swap it for a photocell fitting designed for the purpose.
     
    • Like Like x 1
  10. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    That is unsuitable for an outside light/photocell set up, you should install a seperate unit for a standalone photocell or a photocell built in to a suitable fitting.
     
    • Like Like x 1