Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Earth fault loop impedance, initial verification, multiple DB in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Gary Tollison
    Offline

    Gary Tollison Regular EF Member

    Location:
    Peterborough
    Hello.
    Not sure if this is the correct forum to post this in (still trying to work out where the trainee section is).

    Just been doing some practice fault-finding online.
    Found this scenario:

    After doing initial verification on an outbuilding with its own DB, which is supplied from the main DB in another building, the EFLI on a DB in another building also supplied from the main DB is poor as a result of the I.V.

    I’ve been scratching my head trying to suss out a cause.
    The only one I can come up with is when EFLI was tested during I.V, the main earthing conductor would have to be disconnected to do the test, and then reconnected afterward. The connection wasn’t tightened, resulting in high resistance, yes?

    Thanks in advance
    And btw, any help in how/where to join the trainee section?
    :)
    Gary
     
  2. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Readings ?

    Supply type?
     
    • Optimistic Optimistic x 1
  3. haptism
    Offline

    haptism Regular EF Member

    Location:
    SW. London
    Dont see how a poor loop reading can be the result of an initial verification per se. whatever is causing a high loop reading could be anything from, ccc too small, high resistance (loose) connections, suppliers earthing system at fault maybe, earth rod problems, ect ect. The question does not give enough information imo
     
    • Agree Agree x 1
  4. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Click on the ‘forums’heading at the top of the page , scroll down the page and they will be an option to join the trainee section.
    You just need to fill out a few details etc :)
     
  5. Gary Tollison
    Offline

    Gary Tollison Regular EF Member

    Location:
    Peterborough
    Thanks Ian :)
    As to my scenario, I misread it in my usual fashion!
    The I.V was on the entire installation, not on just one sub DB.
    So it’s most likely damaged cable,or too small.
    Example didn’t give readings, just said what would be the likely cause.
    Thanks for the comments :)
     
    • Like Like x 1
Loading...
Similar Threads - Earth fault loop Forum Date
6A MCB Tripping on Earth Fault Loop Impedance Test Electrical Forum Nov 19, 2018
earth fault loop impedance calculation Electrical Forum Oct 30, 2018

Share This Page

Users found this page by searching for:

  1. fault loop impedance verification

Electricians Directory Post a Domestic Job Post a Commercial Job