Discuss Earth Faulth Loop Impedance HELP!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
17
Hi can somebody shed some light upon correction factors for earth fault loop impedance. I know that the vales of zs in bs 7671 are if the conductors are running at max temp ie worst case scenario , am I right in believing that if you get a measured result you apply 0.8 to it?
 
Also ive got a question im struggling with . ........If an earth fault loop impedance tester measures a value of 0.55 ohms at 20 degrees c, what is the corrected value (using the rule of thumb method) to allow for conductor maximum operating temperature. its gives the answer 0.69 but if I use the rule of thumb method I do 0.55x0.8=0.44 ????????? just a little confused
 
The BGB is a design document, check your Zs from the BGB against the same device in in the OSG
 
You are measuring a resistance when you measure Zs, think about how resistance works:
When the conductor gets hotter the resistance increases.

When you measure Zs the conductors are at ambient temperature, if they were at 70°C the resistance would be higher.

Say you have a measured value of 0.5 then the resistance will be greater than 0.5 at 70°C therefore multiply by 1.2.

If you have a Zs value of 0.6 in BS7671 then the resistance when measured could be lower (so that on heating the resistance rises to 0.6) therefore multiply the 0.6 by 0.8 (the rule of thumb).
1 / 0.8 is approx 1.2.
 
Also ive got a question im struggling with . ........If an earth fault loop impedance tester measures a value of 0.55 ohms at 20 degrees c, what is the corrected value (using the rule of thumb method) to allow for conductor maximum operating temperature. its gives the answer 0.69 but if I use the rule of thumb method I do 0.55x0.8=0.44 ????????? just a little confused


because the resistance increases with temperature rise, you divide by 0.8, not multiply. to correct from 20deg. to 70deg.
 
Thanks for all the replys i think im beginning to get it, @farmelectrics i know therd in the osg but i wanted to know why and how i got them results so cheers for the help guys :)
 
Can't say i've ever used the 0.8 correction factor, except within areas that has typically significantly higher working ambient temperatures (few and far between too). Like when is a conductor ever going to even approach 70'c, let alone be normally working at that sort temperature??


But then again, the vast majority of our circuit Zs values will be more than adequate to accommodate applying the 0.8 correction factor anyway!!
 
The regs are a design document, and most sparks day to day will leave it to gather dust in the van. The Zs tables contained are at 70 degrees, so you apply the 0.8 correction factor (if you want the science and calcs it is in Appx 14).

Most sparks will refer to the OSG, which as someone has already said, the tables have been corrected for us, and are at ambient (20 degrees) so that is the figure you need to meet.

You could go on and on, but to be fair a slight rise or drop in ambient temp is not going to make any significant difference to your Zs values, so the ones in the OSG are adequate for most day to day scenarios you will encounter, hence we use the OSG and not the regs. We may on occasion get colder, but seldom do we experience temperatures of more than 30 degrees unless it is a specific installation that does get hot, saunas etc.

Cheers…………Howard
 
but, as eng54 pointed out, how often do you get cables running anywhere near 70deg.? esp. in a domestic setting. this would only happen if the cable was undersized, or on 1 of them god-awful megawatt showers.
 
[FONT=Arial, Helvetica, sans-serif]The 80% rule of thumb is only intended to be applied to a test result taken from an impedance test. You have to ensure that the tested value does not exceed 80% of the tabulated value.[/FONT]

[FONT=Arial, Helvetica, sans-serif]If the value is above 80% of the figure then improve the result this can be done by improving or providing additional earthing. [/FONT]
 
I may be wrong but I was under the impression that the cables could reach 70 degrees under fault conditions (short cct) where the ocpd was to operate and disconnect within the specified time, (0.4s 5 s,etc) thus causing an increase in cable resistance and that's why we de-rate the zs tables by the 'rule of thumb' 0.8. Well it sounds logical to me anyway!
 
I may be wrong but I was under the impression that the cables could reach 70 degrees under fault conditions (short cct) where the ocpd was to operate and disconnect within the specified time, (0.4s 5 s,etc) thus causing an increase in cable resistance and that's why we de-rate the zs tables by the 'rule of thumb' 0.8. Well it sounds logical to me anyway!

Cable operating temperatures and limiting temperatures under fault conditions are two entirely different scenarios...
 

Reply to Earth Faulth Loop Impedance HELP!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
529
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
725
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock