Discuss Earth Leakage Clamp Meter...Why do I need one? in the UK Electrical Forum area at ElectriciansForums.net

What I can’t understand is what is the difference between some of the £300-500 dedicated earth clamp meters and £50-100 clamp meters that measures down to single digit milliamperes, and these are not total crap.

I bought a cheapo one, as recommended by a forum member, a TM-EL9809 for £120. Had it two years, in which time I used it once okay. Next time I came to use it, it went wibble and was apparently unrepairable.

So I went to purchase a Megger one, but they were out of stock. So without now; not sure whether its worth the investment. But if you got wads of cash, I can see them being a useful accessory, bit like a laser level.
 
I've not had to use mine too much but once I had an intermittent tripping issue at a property which I couldn't find with IR testing, with the clamp meter around the main earth I could see that with certain parts of their cooker turned on, the leakage rose drastically. touch screen type cooker so wasn't possible to find this one with it dead, and the only other option as somebody else suggested was set an rcd tester to ramp test and work out leakage that way, this is just quicker, its only a £100 dilog that has 1mA resolution
 
Unless working in electronics, you're unlikely to need accuracy to greater than 1mA. The meters with a higher top end range are of course also good for current draw measurements, as well as earth leakage, although sometimes the jaws may be too large to work around tight/densely cabled areas, e.g. Megger IClamp. An iFlex or similar device could be better in such cases.
 
I've not had to use mine too much but once I had an intermittent tripping issue at a property which I couldn't find with IR testing, with the clamp meter around the main earth I could see that with certain parts of their cooker turned on, the leakage rose drastically. touch screen type cooker so wasn't possible to find this one with it dead, and the only other option as somebody else suggested was set an rcd tester to ramp test and work out leakage that way, this is just quicker, its only a £100 dilog that has 1mA resolution
Don't clamp the earth connection, you can get false readings.
Clamp both live conductors that way the meter measures what the RCD "sees".
 
I actually use one of these, it's not officially sold as an earth leakage clamp meter but it performs well in the >5mA range. It means I don't need to carry two clamp meters unless the DB is over 400A plus the flexible clamp makes it very easy to clamp phase+neutral or 3 phases + neutral without too much manoevering of the conductors.
Chauvin Arnoux MA400D-170 Clamp Meter, Max Current 399.9A ac CAT IV 600 V | P01120575Z | RS Components - https://za.rs-online.com/web/p/clampmeters/7781040/

I have an earth leakage clamp as well for the odd occasion I need to accurately measure a value that's less than 5mA but I probably haven't used it in the last 6 months.

01.jpg

They do several models with higher current ranges and longer Rogowski clamps.
You'll probably find it cheaper in one of the UK based wholesalers.
 
It looks like for the time being I'll remain without an earth leakage clamp meter then. I can see in times ahead of RCD everything everywhere that it will have it's uses, but I'm failing to see how spending several hundred quid + annual calibration costs will even see one pay for itself, and it seems that it's not going to be an item that gets much if any use throughout the year.
 
It looks like for the time being I'll remain without an earth leakage clamp meter then. I can see in times ahead of RCD everything everywhere that it will have it's uses, but I'm failing to see how spending several hundred quid + annual calibration costs will even see one pay for itself, and it seems that it's not going to be an item that gets much if any use throughout the year.
Not sure it would need calibration.
Perhaps if you were using readings from it to fill in certificates.
 
agreed that is best but my little dilog one wont fit around 2x 25mm tails, I still saw a controlled and consistent increase in leakage clamped around the main earth
i have same problem with mine. clamp won't close round 25mm tails.
 
Millamp clamp meter or a good quality multimeter with low milliamp range connect on line with the earth/CPC works well. With the increase in RCD/RCBO protection being required for all circuits in the 18th edition. We will all have more nuisance tripping RCD faults to investigate
 
Excellent educational video.. thanks for sharing that.
I have to say I do own such a clamp meter but have yet to use it in anger.. it's at the bottom of my Spare toolbar somewhere... I Hope!
Circuit isolation, appliance isolation (usually cooker or immersion element) MFT and a bit of logic has always sufficed to date.. but also am aware of the increase in electronic gizmos can have an a cumulative effect.
 
Millamp clamp meter or a good quality multimeter with low milliamp range connect on line with the earth/CPC works well...

If I've understood you correctly, powering up an installation with a multimeter in series with a cpc or earthing conductor is a bad idea. If the multimeter internal fuse pops, you lose the earth and the exposed conductive parts are likely to rise to 230V.
 
I've had the lend of a Megger Earth Leakage Clamp Meter for a few days. Had a play around with it although typically no call outs...until today. Trying to wrap up for holiday a man down and they poured in. A good day to try it out, but my word, it's absolutely useless for everyday fault finding. It was my IR tester all the way. And damp and water ingress each time .

Its not something I think I'll ever need, it may have its uses as RCD everything gets ramped up and into commercial/industrial premises, but I have no use for it currently.
 
To be honest, you’d probably only use it for nuisance tripping RCDs. Check how much earth leakage there is on a circuit in normal use.
Another use would be to check whether the loading on a 3 phase installation was out of balance.
 
In my experience 50% of RCD tripping is to an earth other than the CPC and I don't think I've ever put a clamp on an earth cable while looking for such a fault.
 

Reply to Earth Leakage Clamp Meter...Why do I need one? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
420
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
I recently borrowed one of these to diagnose an earth leakage problem, and it was very useful: 560 60A Digital Earth Leakage Clamp Meter -...
Replies
26
Views
4K
While waiting for a reasonably priced earth leakage clamp meter that will do both AC and DC leakage, I find myself asking the question which is...
Replies
24
Views
5K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock