Discuss Earth leakage measurement in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
can you touch the terminals of line and neutral with probes what setting would you choose??? i think no, but go on smack me baby
I've got an ordinary fluke clamp meter wouldn't that do or is there a special earth leakage clamp meter available?
That'll be a no then! You measure the earth leakage on the cpc with a clamp meter.can you touch the terminals of line and neutral with probes what setting would you choose??? i think no, but go on smack me baby
so just ac setting on a normal clamp meter on earth conductor, so the leakage tester is just another toy
if you would just go do a days graft telectrix u could have ten , cause you do live electricity
so do you all have earth leakage tester, how much
A "normal" clamp meter will probably not have a fine enough resolution for earth leakage. If you think about what you're measuring it's usually the amount of current necessary to make a rcd/rcbo trip (very often around the 2x milliamp area ... even though they're rated at 30ma most will trip less than that). Remember right tool for the right job.so just ac setting on a normal clamp meter on earth conductor, so the leakage tester is just another toy
Reply to Earth leakage measurement in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net