Discuss Earth leakage on MEC during 'black-out' in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
747
I was recently playing with my Amecal leakage current tester and found approx. 2mA when clamped around both tails at home, I put this down to the various tv's and game consoles on at the time, but when I clamped the MEC at the same time I found a fluctuating leakage current of anything between 200 and 300mA. The house is only about 50mtrs from the sub station (TNS btw and a Ze of 0.2 ohms) This has been bothering me for a couple of weeks now but last night we (the whole village) suffered a power outage for a couple of hours, ideal time me thinks for another test on the MEC, this time I measured a fluctuating current between 10 to 35mA and nothing on the tails (no surprise there!). I'm a little baffled now, could it be a pv system that is causing the leakage from a discharging inverter capacitor or perhaps the pv system generating as it was a full moon last night (not sure if moonlight would be strong enough to do this though.) Has anyone come across this situation before and found where the leakage is from.
Oh, I forgot to mention I disconnected the earth bonding to both gas and water and the leakage dropped to zero but went back up when either was reconnected. No voltage was present between the MEC and earth bonding conductors when separated which makes me think either it's 'ghost currents' (but never ever heard of this lol) or I've got myself a carp leakage tester or should I be worried and get the DNO involved?
Sorry for such a long post but I've tried to give as much info as poss.
 
Hi dude,what type of property is it? Also,has everybody got the same type of supply,are there any PV installations,and did you get any PEFC and PSSC results? Also,fair play to you for messing with your tester whilst everybody else is typing pap on faceboob :conehead:
 
End terrace. Not sure if they have all got the same now as over the last 5 years 8 of my neighbours have had their supply cables replace due to loss of supply so they may have been pme'd but can't be sure. PEFC 1.1kA and PSSC 0.8kA.
 
So you've got a few hundred mA flowing between one big network of conductors and another, when they are solidly connected together, but only tens of mA when the supply is off. Doesn't sound terribly surprising or worrying to me. If it were 100 times higher I'd start to pay closer attention.
 
But it's not leakage current, that was only 2mA when you clamped the tails. The rest of it is just circulating ground network current, driven by negligible voltage over low external impedances, as per your test with the voltmeter with the bonding open-circuit.
 

Reply to Earth leakage on MEC during 'black-out' in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
1
Views
952
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock