Discuss Earth/Neutral fault..Help Needed!! in the UK Electrical Forum area at ElectriciansForums.net

Hi,i'll be honest,if i was attempting to explain a situation to a customer,in a property with a suspected earth issue,disconnecting the neutral tail,and leaving the line connected,would not be a method i would choose.

This is a situation,which would be considered dangerous,in an older property,where earths at origin,may be poor,and an original fused neutral,had blown.
 
Hi,i'll be honest,if i was attempting to explain a situation to a customer,in a property with a suspected earth issue,disconnecting the neutral tail,and leaving the line connected,would not be a method i would choose.

This is a situation,which would be considered dangerous,in an older property,where earths at origin,may be poor,and an original fused neutral,had blown.
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?
 
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?

I too do not like irrelevant or negative coments when asking a legitimate question, but I think you need to re read pegs posts as they are relevant and I couldn’t detect any negativity other than stating concern over a potentially dangerous issue.

In the past we have had on this forum, if you don’t know you shouldn’t be doing it. It’s changed.

all the posts have been in order to help. Re read them.
 
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?

The best advice I'd give to start with is that you stop creating dangerous situations by disconnecting the neutral of a live installation.
As lucian has pointed out this will have diverted the load current via the fault to earth and potentially caused a lot of damage in doing so, not to mention the significant danger to your life and that of anyone else in the property.
 
How does this explain disconnecting the neutral tail coming out of the meter and the board still being live across L-N?
Oh dear. You need to read it again.
You've made no mention of isolating the incoming L so we have to assume that's at around 240V relative to earth and incoming N.
You've disconnected the N.
You measure between the 240V L and something that is now "sort of floating" with various resistive and capacitative paths (one of which is your meter) to both L and E.
So the N will be at some voltage between E and L - and you are measuring the difference between that and L.
 
This thread is making my head hurt. I've read it start to finish and back to front. Still can't work out what the heck is going on
 
Hi dude,i apologise if i have offended you,but your original post title,was regarding the earthing. You were asked several times,including by myself,regarding this,and got no answer.

I am sorry you think my points regarding the safety aspect of disconnecting and then demonstrating,are irrelevant....this is a worry.

I wish you well and success in your quest,but as the great Deborah Meaden said....i'm out?
 

Reply to Earth/Neutral fault..Help Needed!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
966
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock