What is the means of earth fault protection to the SWA's?
Has a main adjustable RCD
[automerge]1579416233[/automerge]
It’s an overhead 3 phase supply, looking at the electric board cut out there’s no earth there eg TNS or PME, but at the other end of the tails connected to a DB there’s an earth there, tested that at 17.5 ohms and connected in parallel with all other DBs and it’s 0.60 ohms, then my highest sub circuit is about 1.57 ohms
 

Reply to Earth readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
414
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
509
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock