Discuss Earth spike , through wall? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
60
Hi all,

Just fitted a car charger , I need to put an earth spike in but having trouble siting it, the main consumer unit is on the garage wall , directly behind it is earth as the garage is set into the hill if you know what I mean so if I drill through the wall I will hit the mud, is it ok to then hammer the rods in so the rod will be out in horizontal and the rod box fitted on the wall underneath the consumer unit?.

Cheers
Grand
 
They need to keep track of every EV Charger installation due to overloading the system. Hence the legal requirement to register. See code of practice for electric vehicle charging equipment installations by the IET. The main book for us to follow along with BS7671
 
They need to keep track of every EV Charger installation due to overloading the system. Hence the legal requirement to register. See code of practice for electric vehicle charging equipment installations by the IET. The main book for us to follow along with BS7671

That’s lovely, but the thread is about earth electrodes.
 
They need to keep track of every EV Charger installation due to overloading the system. Hence the legal requirement to register. See code of practice for electric vehicle charging equipment installations by the IET. The main book for us to follow along with BS7671

Which law requires this? Can you provide a link to the act of parliament concerned?
 
They need to keep track of every EV Charger installation due to overloading the system. Hence the legal requirement to register. See code of practice for electric vehicle charging equipment installations by the IET. The main book for us to follow along with BS7671

Could you provide a link? I'm intrigued as I've never heard of this before!
 
As you are asking these questions how are you testing your installation as a normal MFT is not sufficient for the job. Either the Seaward EL-100 / Rolec tester or similar is required. The tester pretends to be the vehicle and does a handshaking exercise this proves install is safe & fit for purpose. Cant use the car as the tester as could be an expensive repair or potentially dangerous.
 
Spinlondon make a comment on usage of earth rod. The earthing arrangement for the installation has not been confirmed on the start of this thread. Suggest you make sure of the earthing arangement first then apply the regs. For simple explanation buy the book above or go to BS7671
 
Spinlondon make a comment on usage of earth rod. The earthing arrangement for the installation has not been confirmed on the start of this thread. Suggest you make sure of the earthing arangement first then apply the regs. For simple explanation buy the book above or go to BS7671
Not sure if this post was directed at me, or just mentioned me?
Also not sure whether the Installation Earthing arrangement is relevant.
From what I understand in this instance, the charging point is inside and is not for public use.
Perhaps to save me from having to purchase any literature, someone could explain why an Earth electrode would be necessary in this instance?
 
The following is a generalism for external EV chargers. The regs should be followed however it’s roughly the following. If it’s TNS and likely to be changed to PME then ev charger should have earth stake. If it’s PME then it must be earth stake. If it’s guaranteed TNS no earth stake. If it’s integral garage EV charger bonded to MET along with anything else in close proximity should have supplementary bonding hope that makes sense.
 

Reply to Earth spike , through wall? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
810
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
780
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock