Having just changed the first c/u in 20 years for my part p inspection i have encountered a fault which has to be sorted.
Ive replaced an old wylex fused 6 way unit and installed a split load board.
System comprises of lights up, lights down, immersion, cooker, shower and ring.
PME system with 6mm earth to gas and main earth at pme.
There was another earth leaving the old board which didnt seem to go anywhere as tests between old c/u earth terminals and pipes before i started gave very poor readings.
New 16mm to pme, new 10mm to gas and cold mains at stop tap.
Several accessories need replacing.
Now I have continuity between ring RN and R2 on both legs of ring and continuity between RN and main earth im guessing because i have installed a new earth to the cold mains.
When I carried out a resistance test on R1 R2 and RN I got even readings on R1 and RN but R2 was more then double. The cpc is only 1mm.
I then carried out a test on entire ring on R2 and worked out the cable route and the readings jump by .20 ohms between 3 accessories in the middle of the ring where a spur has been connected.
All the wiring is original but it seems a few accessories were done in spurs (heating and garage to name a few)
If the fault is just at an acessorary (plate screw in contact with RN) i can understand the continuity between RN and R2, however there is continuity between RN and main earth terminal even with the 2 legs of the ring completely disconected from the c/u.
The only explanation for this I can think of is a damaged cable in direct contact with a pipe (now correctly earthed) however the R1 and RN readings were identical within .01 and I would have thought this would have shown up a differantly if there was contact of N to earth.
Tomorrow (sunday) I shall inspect all accessories but am worried it may be a fault under the floor.
I hope this makes sence and someone can give me some advice.
Many thanks
Ive replaced an old wylex fused 6 way unit and installed a split load board.
System comprises of lights up, lights down, immersion, cooker, shower and ring.
PME system with 6mm earth to gas and main earth at pme.
There was another earth leaving the old board which didnt seem to go anywhere as tests between old c/u earth terminals and pipes before i started gave very poor readings.
New 16mm to pme, new 10mm to gas and cold mains at stop tap.
Several accessories need replacing.
Now I have continuity between ring RN and R2 on both legs of ring and continuity between RN and main earth im guessing because i have installed a new earth to the cold mains.
When I carried out a resistance test on R1 R2 and RN I got even readings on R1 and RN but R2 was more then double. The cpc is only 1mm.
I then carried out a test on entire ring on R2 and worked out the cable route and the readings jump by .20 ohms between 3 accessories in the middle of the ring where a spur has been connected.
All the wiring is original but it seems a few accessories were done in spurs (heating and garage to name a few)
If the fault is just at an acessorary (plate screw in contact with RN) i can understand the continuity between RN and R2, however there is continuity between RN and main earth terminal even with the 2 legs of the ring completely disconected from the c/u.
The only explanation for this I can think of is a damaged cable in direct contact with a pipe (now correctly earthed) however the R1 and RN readings were identical within .01 and I would have thought this would have shown up a differantly if there was contact of N to earth.
Tomorrow (sunday) I shall inspect all accessories but am worried it may be a fault under the floor.
I hope this makes sence and someone can give me some advice.