Copied and pasted a reply from the other forum contains a lot of info! Deffo same OP as same pictures etc this is from the cert.

Quote

"OK, let's see.... It's pretty much Greek to me, but I'll give you what I think might be relevant!

TN-C-S.

1-phase (2 wire)

Means of earth - Distributor's facility

Installation earth electrode - either says MA or NA.

Conductor material - copper

Condutcor CSA - 10.00mm2

Water service box = ticked

Oil service box = ticked



Do you need anything else?


Cheers"
 
So it looks like he's 'bonded' the oil pipe by earthing it? Daz.
 
Sounds like it ... total lack of understanding oil pipes are generally sheathed so its highly likely he's made the installation less safe than it was

Sheathed or not, he's earthed rather than bond back to the MET. Total misunderstanding! Daz
 
None at all, I suspect the person who did it has no idea as to the theory behind it.
Me too. The tank looks like it's plastic from the photo so the rod would only be serving the buried pipe. The way it's connected to the pipe doesn't look like it was intended as an earth point for a bulk supply truck to attach a trailing earth clamp for safety during the filling process so I'm stumped....

The missing bolt is also making me skittish. I've seen enough from the photos to second the advice of getting an experienced sparky to check it out and ramp test the RCD whilst he's there.
 
If the supply to the premises is TN C S I hope it's already PME'd otherwise that pipe might get warm if there's every a DNO joint fault :)
 
Only thing I can think of is as the oil pipe was bonded to the met inside the building and TNCS perhaps there was a touch voltage on the oil pipe at the tank between it and true earth ?
 
Hi all

I thought I was up to date on the thread on here. Just come back and there's a page worth of posts I didn't realise were there! I guess that's the potential when you post on several forums :oops:

Anyhow, many thanks for all the posts and help. I emailed the electrician (being xmas and all) and haven't heard back. I think in the New year I'll give him a call and see what he says as to why he fitted the rod and earthed the tank. No one seems to understand why he done it. We recently had an electrician over to fit a new cooker. They had a quick look and couldn't see why he had bothered either. Not that it was entirely pointless, more just an extreme case of belt and braces!

One thought.... Our mains water comes into the house via a blue plastic pipe rather than metal. Could that be anything to do with it? Could it be that he could not earth it to the house's pipework and so had to use the rod? Please bear in mind that this is a totally uneducated stab in the dark!

Cheers for all the help.

PS - the electrician who came also ran a test on the RCD that wasn't working initially. He said it is absolutely fine.
 
That's why I said total lack of understanding..... chances are the pipework wasn't extraeneous to start with due to sheathing and a plastic bund. that is until the sparky made it so !

So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!
 
So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!

But he hasn't bonded it. He's earthed it with a rod. Daz.
 
If it's not bonded at the other end and connected to the MET then earthing it via its own rod could cause issues in the equipotential zone of the main installation. Also, connecting it via bonding to the MET could be an issue if the installation earthing arrangement isn't PME'd by the DNO.
 
If the oil pipe is bonded in the house then the earth rod connected @ tank end is not creating a danger nor has it any use, classic example of somebody doing something without knowing why or what there trying to achieve.
 
That's funny because on TT systems I often say the conductor to the rod is doing just that, earthing the rod. Take it away it will probably make no difference.
 
So you wouldnt bond that buried oil pipe because it has a plastic covering? What happens when the plastic gets damaged or breaks down and the pipe is then extraneous?! Rediculous.. bond it!

I would bond at the point of entry to the property I would not Earth it with an earthrod. My suggestion is that the addition of the earth rod has more than likely made the installation less safe
 

Reply to Earth wire on domestic heating oil tank - various questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock