Discuss Earthing a scaffold any suggestions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
A local church is going through some refurbishment, it currently has a mass of scaffolding in one position.

I have been asked to earth it... my initial thinking would be TT spikes on all 4 corners?
 
Not knowing a lot about this but is it the norm to earth scaffolding?
 
I would have expected that the scaffolding should be bonded to the earthing system of the church and the lightning protection, if present; to earth the scaffold would be simply to ensure that if some had a shock from the scaffold it would be very serious rather than serious, though it might ensure an RCD's operation.
To bond you would need to ensure the scaffolding was electrically continuous and then run a suitably sized bonding cable from the scaffold (possibly at two places for reliability) to the MET / bonding or lightning protection.
 
If it was a regular thing to do, there would be official products such as "scaffold bonding clamps" or something.
The construction of scaffold doesn't lend well to being an earthing conductor. Painted metal, slotted into each other.
The impedence between the top of the platform and where any main bonding could be too high to be of any benefit.

I cannot recall any mention in the BYB of earthing a scaffold
 
Here are the parts from BS7430.
20180417_103722.jpg
20180417_103704.jpg
20180417_103647.jpg
20180417_103733.jpg

They have come out in the wrong order, read 3, 2, 1 and 4.
 
It should be noted the above is from an old copy of BS 7430 but generally there are no changes from the above. It is no longer Reg 22 but Reg 8.
 
Paragraph 8 Text as text:
8 Special installations
8.1 Temporary scaffolding and similar metallic structures
8.1.1 Metallic structures assembled by means of bolted joints or screw
clamps
NOTE 1 Where structures are assembled using bolted joints or screw clamps a multiplicity of such connections is likely to provide several paths of relatively low resistance. Although such structures are not designed to be electrically continuous it is reasonable to assume that they have a low value of electrical resistance.
Whatever type of structural fastenings or footings in contact with the ground are employed and however a temporary structure may be fastened to a permanent structure, it should not be assumed that a temporary metallic structure is effectively earthed.
NOTE 2 Most erections of metallic scaffolding are the subject of statutory regulations concerning construction work.
The distribution of electricity on construction sites should conform to BS7375. Except where it is necessary for lightning protection purposes (see 8.2), scaffolding external to a structure should not be connected to the means of earthing within the structure that is afforded by supply authorities.
Where scaffolding is erected against or around a structure which does not have electrical services, and electrical equipment is not likely to be used for construction work, electrical bonding for shock protection purposes may be omitted.
Where protective conductors are required, they should be of copper and protected against corrosion by a covering at least equivalent to the insulation of a single non-sheathed cable, and should be routed to avoid damage from work equipment and work activities. A conductor should be connected to scaffolding by a corrosion-resistant clamp conforming to BS951, and which is suitably protected against mechanical damage. For extensive scaffolding structures, where earthed, connections should be made at points not more than 20 m apart laterally.
8.1.2 Structures forming part of precautions to avoid danger from live overhead electric lines
COMMENTARY ON 8.1.2
The Health and Safety Executive publishes guidance on the dangers of live overhead
powerlines, see Guidance Note GS6 Avoidance of Danger from Overhead Electrical Lines[5].
Paragraph 20 b) of GS6 refers to the use of a tensioned wire fence as a high level
barrier, and notes that the electricity distributor has to be consulted about the erection and earthing of the barrier.

8.2 Lightning protection
If scaffolding is associated with an existing structure which has an external lightning protection system (LPS), it should be bonded to the earth termination network and the air termination network of the LPS. Lightning protection should otherwise be provided where indicated by risk assessment performed in accordance with BSEN62305
 
If I recall correctly BS62305 covers lightning protection. And if the Church had protection deployed and was still damaged, then bet those lovely insurance folk would make a case that only God could defeat BS62305 so it's clearly an act of God, so no need to pay out ...
 
It was inevitable that tel would post a link to that song.
 
Hi,who has asked you to "alter" this scaffolding?

The outfit responsible for erecting it,and whoever commissioned it,would or should have done a risk assessment,and any requirement to earth/bond or otherwise modify the structure,would be in that.

You cannot start clamping cables to a structure which at end of build up,and on a daily basis,should be inspected visually,to conform to exactly what was commissioned and agreed.

There could be a discussion regarding any unauthorised work,such as this,as introducing a potential electrical risk,where there was not one previously.

This is a common issue,with large,long-running refurbs,on churches,community halls,scout halls,etc,where "bob" on the committee,who did a bit of electrical work when working,mentions during a meeting,that there needs some "earthing",and he can sort it...

If i am wrong,i apologise,which means there is a request through specification,in which case,simply follow that directive.
 

Reply to Earthing a scaffold any suggestions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
426
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
486
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
544
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock