Morning all - this is something im currently looking into but don't have much experience in myself.

To clarify; Does the mains earthing arrangement need to be switched in the changeover switch to a TT system when the generator is used as the mains supply?

Everyone I have spoken to has only ever seen 3pole + switched neutral change over switches so I'm unsure of what is the best way to complete the works.
 
I think post 5 sums it up. You must not rely on the DNO supply for an earth when using the genny, but probably don't need to disconnect it either. Ask the DNO.

to a TT system when the generator is used as the mains supply?

Having an earth rod at the genny doesn't make it TT. The earth terminal of the genny is referenced to real earth by the rod but the installation MET connects to that terminal by a cable, which makes it TN-S. Fault current from the installation flows through the cable, not the rod. It would only be TT if the genny had a rod and the installation had a rod, and the only connection between the two was the mass of earth, which is daft.
 
Just to add that often generators have output RCD in case they are used with sockets (stand alone supply) but also often to make sure they disconnect quickly as the PFC on a real fault from the generator is going to be far short of the grid's capacity. It that context they look a little like a TT supply, but as @Lucien Nunes points out, really are TN-S.
 
BS7430 is the reference for this - a genny servicing a building should be connected to that building's MET.
 

Reply to Earthing arrangements to a generator and change over switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
532
Afternoon! Hoping someone has experience working on the ABB gear below. It’s in a Mobile Office/ Welfare unit, supplied via either 230v hook up...
Replies
0
Views
211
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K
Hi Sorry to bring this one up again but have read numerous posts and answers and not got an answer specific to my situation. I have a Loncin...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock