Discuss Earthing equation 3P 100A in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi guys

I carried out an EICR a while back on a property with 3P 100A incomer and it only had a 16mm earth. I thought this was undersized, I made contact with the local DNO and had 2 replies, one said it was fine, the other said it should be 25mm.

Im trying to do the adiabatic equation for it, but its so long since I did one of these I want to ensure im getting it right.

S=(⎷(I2t))/k

so I being the possible fault current which was 2.4kA, 2400 squared is 5760000

t being the disconnection time, which for a BS88-2 at 2.4kA is 0.1

K being 143

im getting ⎷(5760000 x 0.1) = 758.95

758.95/143 = 5.3mm

5.3mm seems far too low, what have I missed?
 
what's the PEFC? ( not PSCC). that's the value you need. and what csa are the L1, L2,and L3 conductors?
 
Been puzzling that Vorti, not saying you are wrong can you expand a little please
I stand corrected in fact the square root has been applied, bit trigger happy there. Have been a bit quiet lately due to just moved into our new home in a new town. Lovely five bed semi Victorian villa with an old victorian built double garage in a private lane at the back. Just about got unpacked a week later. Anyway yes definitely wrong on that one.
 
I carried out an EICR a while back on a property with 3P 100A incomer and it only had a 16mm earth. I thought this was undersized, I made contact with the local DNO and had 2 replies, one said it was fine, the other said it should be 25mm.

5.3mm seems far too low, what have I missed?

You don't even need to do the calculation for this, just look at table 54.7 in bs7671.

Based on experience 5.3mm is the kind of size that can normally be expected from the adiabatic equation on small supplies like this.
 

Reply to Earthing equation 3P 100A in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock