My customer wants to have one ring main connected via a change over switch to a generator.

Earthing is TNCS

My idea was is move the ring main to a new consumer unit run a 6mm T&E to the change over switch from the 32 amp mcb in the main C/U where the ring main was. Then a 6mm T&E back from the change over switch to the new C/U.

I would install an earth rod which would be connected to the new C/U so the new C/U would have two earths one from the existing C/U and one from the earth rod.

The house is in a village with lots of overhead wires and I just thought what would happen if the neutral was brought down by a tractor then the return current that would normally go down the neutral of all of the houses after the break would be back fed through my customers C/U through the ring mains T&E and to ground via the earth rod. This could easily be a very high current which would surely melt the earth wires of the ring main.

Am I missing something ?
 
so you are using the earth separate ?
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
 
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
now the I get the story.
 
My idea was is move the ring main to a new consumer unit run a 6mm T&E to the change over switch from the 32 amp mcb in the main C/U where the ring main was. Then a 6mm T&E back from the change over switch to the new C/U.

I would install an earth rod which would be connected to the new C/U so the new C/U would have two earths one from the existing C/U and one from the earth rod.

The house is in a village with lots of overhead wires and I just thought what would happen if the neutral was brought down by a tractor then the return current that would normally go down the neutral of all of the houses after the break would be back fed through my customers C/U through the ring mains T&E and to ground via the earth rod. This could easily be a very high current which would surely melt the earth wires of the ring main.
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.

Am I missing something ?
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
 
it would flow down the neutral after the break into my customers house at which point the neutral and earth are linked together, then to the existing C/U then to the CPC of the ring which is linked to the earth rod.

Hope that make sense !

But that wouldn’t flow through the cpc of the ring circuit, it would flow via the earthing conductor and cpc to the changeover switch, then to the essential services CU, then to the earth electrode.

Whatever position the changeover switch is in, as you have described it, the route from the N-E link in the cutout to the earth electrode will always be via the 6mm T&E’s rather than via any final circuit.
 
Not applicable here, but on a larger standby set, where there is an N-E link, am I correct in thinking the generator earth should be connected to the MET of the installation? (as there will be times when both genset and DNO supplies are energised concurrently, e.g. after the DNO supply is restored following an outage, prior to the AMF changeover switch reverting to the DNO supply)
 

Reply to Earthing Generator TNCS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
541
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
772
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
355
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
307
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock