Discuss earthing systems with standby generators in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

gjaggers

i have a 230v system connected to a tncs earthing arrangement and have been asked to connect a standby generator,i believe the generator should be connected to a tt earthing arrangement so how should i go about connecting the 2 two different earthing systems together
the boss has said just connect the earth rod to the tncs system ,a cardinal sin in my eyes!!!!!!
should i rearrange the tncs system to a tt type?
 
It is my understanding that your boss is correct, the DNO earth is required to be bonded to your earth electrode and hence to the generator starpoint.

I seem to recall a 3-pole changeover switch being acceptable on a DNO TN-C-S system changeover switch, 4-pole on TN-S.

It was explained to me that any utility work on the neutral conductor, cable sheath or substation earth electrodes already takes into account the risk of transfer potential due to unbalanced generators, poorly wired (reverse polarity) installations and genuine earth faults as part of published live working procedures.

As always, check on local DNO requirements and the ESQCR 2002 Regulations
 
Well when the genny is running, assuming it is not a floating power supply (i.e. neutral isolated from earth in the genny?), the star point / neutral is connected to gen frame which is in turn earthed through the rod(s) you will have installed.;)

Think of a line to earth fault of a circuit supplied by the genny - the fault current will flow from the genny line, down through the circuit, through the fault, and will return through the SWA (or 3rd core) to the genny star point thus operating any protective devices in the geney. Generator outputs are by and large TN-S systems, because you are running an actual CPC in the cable, the fault current has no reason to go anywhere else other than back to its origin.

Any fault should not flow through the main supply earthing as they are not referenced together other than at their orgins via earth rods into the rock we all live on.

Likewise the rods on the gen frame ordinarily would not form part of the earth fault path of the geney system unless your installed CPC was damaged.

IMO leave all earthing connected together.
 

Reply to earthing systems with standby generators in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
547

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock