Discuss EIC or MINOR WORKS? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
26
HI EVERYONE, IF I ADD A RADIAL CIRCUIT OF 2 SOCKETS , 5 METER RUN IN 4MM FLEX CONTAINED IN CONUIT AND TRUNKING, AND TERMINATE IT IN AN EXISTING 32AMP MCB WHICH SERVES A RING CIRCUIT, DOES IT WARRANT A MINOR WORKS OR EIC CERT? I UNDERSTAND THAT IF I PUT IT ON ITS OWN BREAKER IT WOULD BE AN EIC , BUT WHAT ABOUT IN THIS SITUATION WHERE I AM ESSENTIALLY ADDING TO AN EXISTING CIRCUIT..
THANKS IN ADVANCE. :)
 
Why 4mm² flex? This will not mix well with solid conductors in the MCB.
Also, by doing what you propose, you have altered the nature of the ring final circuit in a way that is not accounted for in appendix 15, which, although it may be perfectly safe, might confound anyone who comes across it in the future.
I would suggest doing as @westward10 says and incorporate the new sockets into the ring.
Or make it a new circuit. (Which, if in a dwelling, would be notifiable to local building control).
 
HI EVERYONE, IF I ADD A RADIAL CIRCUIT OF 2 SOCKETS , 5 METER RUN IN 4MM FLEX CONTAINED IN CONUIT AND TRUNKING, AND TERMINATE IT IN AN EXISTING 32AMP MCB WHICH SERVES A RING CIRCUIT, DOES IT WARRANT A MINOR WORKS OR EIC CERT? I UNDERSTAND THAT IF I PUT IT ON ITS OWN BREAKER IT WOULD BE AN EIC , BUT WHAT ABOUT IN THIS SITUATION WHERE I AM ESSENTIALLY ADDING TO AN EXISTING CIRCUIT..
THANKS IN ADVANCE. :)
Why 4mm flex? 2x sockets should be on a separate radial, unless fed via a FSU.
 
Why 4mm flex? 2x sockets should be on a separate radial, unless fed via a FSU.
that's the correct way, but as he's used 4.0mm for the spur, does it still need fusing down if more than 1 socket???esp.ashe's fed it from source and not putting excessive load on 1 point of the circuit.
 
that's the correct way, but as he's used 4.0mm for the spur, does it still need fusing down if more than 1 socket???esp.ashe's fed it from source and not putting excessive load on 1 point of the circuit.
A spur constitutes 1 twin or 1 single SO, NOT 2 sockets, if the RFC he is coming from is 2.5mm then why use 4mm, maybe that;s all he had, seeing as he doesn't answer I guess we will never know.
 
Not a spur as such though. If I've read it correctly he is wanting to put a 4mm radial circuit in the same OCPD as an existing ring circuit.

As someone said above, either extend the ring or put the new circuit in a separate MCB.
 
give us a chance :)
4mm flex is the cable I have to hand,the run is in containment.
I'm not fusing down via a FCU as the 4mm cable is big enough,If I were using 2.5mm cable,then I would have a 13amp FCU before the two sockets.
The question I'm really asking is , does it need to be an EIC cert or a MINOR WORKS cert :)
 
Why 4mm² flex? This will not mix well with solid conductors in the MCB.
Also, by doing what you propose, you have altered the nature of the ring final circuit in a way that is not accounted for in appendix 15, which, although it may be perfectly safe, might confound anyone who comes across it in the future.
I would suggest doing as @westward10 says and incorporate the new sockets into the ring.
Or make it a new circuit. (Which, if in a dwelling, would be notifiable to local building control).
thanks for your help, I think I will do as you advise.I was gonna put a new 16mcb in for the circuit but all the L1 phase ports were taken and I didnt want to have them on a different phase to the other sockets in the room (garage).
 

Reply to EIC or MINOR WORKS? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
843
Hi everyone, I’m brand new to the site and hope everyone is doing well. My question is this: I have a 2365 level 2 diploma and have been doing...
Replies
6
Views
1K
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock