Discuss Eicr advise needed please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

1983

-
Reaction score
34
Hi all some advice please been asked to carry out A eicr on a flat the flat is in a care home 27 flats seems like when it was bulit non of them have had a earth run to them jusy l n tails only and the earth is taken from the neutral via a Henley block am I right in saying it's a c2? Going by reg 543.1 It's a pme system
 
Then a PEN conductor is not permitted apart from a DNO supply cable.
Without looking they maybe other exceptions however the set up you are testing it would not be permitted.
How old is the installation?
 
Thanks Ian I gave it a c2 for the reasons u said just wanted to hear others views say good 30 years old install the client is worried as each flat has same issue
 
As far as I'm aware a PEN conductor is permitted on a private supply transformer only which would be the DNOs.
I find the set up you've described quite worrying really if all the flats are like this?
Is there a main earthing conductor at the supply intake were the supply comes in and connects to the metering equipment?
 
Yer there is also main gas and water to bulidmg is bonded to the main met just each flat has no earth got me thinking how did they pass it at the time seem to come across a few in the east London areas
 
Whilst you cannot install a PEN conductor these days, it is permissible to maintain an existing installation and the requirements for such are still in bs7671 as far as I know.
So you can't, to the best of my knowledge, give it a code based purely on it being this type of installation.
 
The problem I got is I need to change the ccu within the flat as well as carrying out a eicr guess I got no choice but to run a 16mm earth in
 
I disagree.
A lost neutral to the flat would result in possible full mains voltage appearing across the cpcs connected directly to the neutral inside the flat.
I believe it to be a potentially dangerous situation the way it is now.
 
That's not quite what I was expecting to see, I thought it was going to be a very old installation from the days when a PEN conductor was acceptable, not an abortion like that.
 
Lol sorry had to laugh the whole install is 30 year old ish submain running to each flat 16mm phase & neutral no earth 27 flats over 3 floors but as u can see nearly all flats have had work carried out in recent years.
 
I find it difficult to believe it has always been like that. The supply conductors look single insulated leading me to believe the original cpc was provided by its containment which is concealed behind the latter dist board, someone has then been connected from the neutral. Where have you got the 30 years from.
 
I find it difficult to believe it has always been like that. The supply conductors look single insulated leading me to believe the original cpc was provided by its containment which is concealed behind the latter dist board, someone has then derived a cpc from the neutral. Where have you got the 30 years from.
 
Maybe the answer lies at the supply end and how they are contained and if the tails are installed along their route perhaps in galv trunking?
 

Reply to Eicr advise needed please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Hi all, new to this forum and am completely clueless with all things electrical - hoping to get some advise! My parents received an...
Replies
11
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I’m sure this has been covered a squillion times before but advice please. EICR on block of 5 flats all with separate electrical supplies &...
Replies
5
Views
1K
Hi, I'm new to being a Landlord (wasn't my plan!) Anyway I contacted a company online who arrange for electricians from around the country to...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock