Discuss EICR and CU change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
5
Hi guys. I have 2 questions to confirm my thinking.


1. If I perform an EICR on an installation, which was Installed whilst a previous edition of the regs were in place, does it mean that I can give a satisfactory condition providing all test results and observations are correct for that particular set of regs. Much the same if I see work was done at a time where RCDS were mandatory for circuits incorporating socket outlets and the installer had not followed current regs at time of installation, that would mean an unsatisfactory condition would be what I would report. Is this correct thinking?

2. If a customer requests a CU change and I notice the lighting circuit had no CPC, would I be able to install new cu, and then test install as usual. Or would I have to rewire lights first to bring up to current regs?

any help would be gratefully received.

Matt.
 
Google electrical safety council and download and READ Best Practice Guide #4

EDIT and the best practice guide that covers the lighting circuit with no CPC.
 
Sombody needs to post a thread with the link to the ESC and these dam guides - they are really important and useful to get consistency across the trade.
 
Sombody needs to post a thread with the link to the ESC and these dam guides - they are really important and useful to get consistency across the trade.

Completely agree Murdoch.

I have linked them many times in threads, however unless you are reading that thread you wont see the link.

Their are perhaps too many stickys already but this would be good to make into one I think (unless it allready is and I just haven't found it!!)
 
Somebody needs to point out you need a good understanding of what too look for during the inspection stage, a good understanding of of the old regulations and how the codes should be applied. Using the ESC guides as a back up and not a be all to everything you may come across as a firm coding.
 
1. If I perform an EICR on an installation, which was Installed whilst a previous edition of the regs were in place, does it mean that I can give a satisfactory condition providing all test results and observations are correct for that particular set of regs.

Not necessarily. It depends entirely on whether or not you judge it to be safe. You are conducting your inspection against the Requirements of the current Edition of the Regulations. It is not relevant whether or not it complied with the Regulations of the time. Would an installation to the 1st Edition be safe to remain in service?
 
Thank you all for your help I will look over guides straight away and get a better understanding of EICRs. Thanks Trev for your useful comment, really helpful. I suppose that's why they create these forums.
 
You are conducting your inspection against the Requirements of the current Edition of the Regulations. It is not relevant whether or not it complied with the Regulations of the time.

I think you may need to read the Note by the Health and Safety Executive in your regs. BYB page 11.
Our interpretation seems to differ.
 
I think you may need to read the Note by the Health and Safety Executive in your regs. BYB page 11.
Our interpretation seems to differ.

I presume this is the note which states that earlier practices are not necessarily unsafe. This clearly suggests that, by the same token, that they are no longer necessarily considered safe either. In other words you need to make a judgement call.

Your inspection is still required to be carried out against the current Standard.
 
I presume this is the note which states that earlier practices are not necessarily unsafe. This clearly suggests that, by the same token, that they are no longer necessarily considered safe either. In other words you need to make a judgement call.

Your inspection is still required to be carried out against the current Standard.

As long as people make the correct judgement call. I don't like people stating that a CU is unsafe just because it's "not to current standards." It comes across like they are trying to deceive the customer.
 
Last edited:
Thank you all for your help I will look over guides straight away and get a better understanding of EICRs. Thanks Trev for your useful comment, really helpful. I suppose that's why they create these forums.

Trev can always be relied on to give sound advice
icon14.png


What I expect he is meaning to say in a very brief post is.

"EICRs are expected to be carried out by electricians with an above average knowledge and with experience of the type of installation being inspected"

Do you satisfy that definition taken from the advice given by the IET ?
 
Trev can always be relied on to give sound advice
icon14.png


What I expect he is meaning to say in a very brief post is.

"EICRs are expected to be carried out by electricians with an above average knowledge and with experience of the type of installation being inspected"

And allow the necessary time to inspect the installation thoroughly

Do you satisfy that definition taken from the advice given by the IET ?

I've edited that for you!
 

Reply to EICR and CU change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
610
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock