These are directly lifted from BPG 4 - EICR's

Items worthy of note that do not warrant a classification code (These comments should be recorded on the EICR in the observations section)

• Presence of a consumer unit or similar switchgear made from combustible material (e.g. plastic) that is not inside a non-combustible enclosure and which is NOT:
• Located under wooden staircase, or
• within a sole route of escape from the premises (Note: If unsatisfactory connections are found during inspection, this would warrant a code C2 classification to be recorded

Items that should not be listed as non-compliances with BS 7671 and do not require reporting (Mythbusting)

• The use of rewireable fuses (where they provide adequate circuit protection)

With regards to not paying, I think you can make a fairly sure-footed argument that the inspector was not able to demonstrate the skills required for the service under contract.
 
Just to note that the Napit guide "Codebreakers" indicates a C2 is warranted where there are cables buried in walls at a depth of less than 50mm, and no RCD protection for those cables. This would apply to the off peak consumer unit cables if there are any such buried cables. As a Napit member, your inspector may feel bound to follow their own guidance.

Then to add a note to counter that note, the BPG4 quoted above would disagree, recommending only a C3.

Unless you can get the inspector to be more specific as to the C2s given which could argue his case, I suspect he's being a little over zealous.
 
The installation is sound and complies with regs. applicable at time of installation.

However an EICR is carried out to current regulations not the regulations that were applicable to the original installation.

One of the reasons an EICR is carried out is to identify things which, due to changes in regulations/technology/our understanding of what is safe, can be improved or need to be improved.

Anything which does not comply but would not offer any appreciable safety improvement if it was changed to make it compliant should not be coded on an EICR.
However anything which does not comply and changing it would improve safety should be coded, regardless of whether it complied at the time of installation.

There are multiple reasons why RCD protection is required for circuits and the different reasons can get different codes.
If one of those circuits feeds a heater in a bathroom or if the supply is TT then there could be a strong argument for a C2.

Also, as posted above, NAPIT's official guidance to their members is to give a C2 for a lack of RCD protection to buried cables. So your electrician may well be following guidance from NAPIT and so your complaint to them won't get you anywhere. Plus if course this information will help them immensely when they take you to court for non-payment.
 

Reply to EICR - Applying regs retrospectively in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
My parents had an EICR completed after a change of tenant in the shop and flat property, this took place March 2021. The summary of the report...
Replies
35
Views
5K
Hi, hopefully, you can help me by giving some guidance over the EICR which has failed for my rented property. It was carried out by an electrician...
Replies
16
Views
4K
Just a rant regarding all these landlords EICRs that have become the in thing. And maybe a word of caution to all of you doing them. To kick off...
Replies
151
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock